gazj82
I meant per socket outlet!! Not per double socket!! Jesus!
My point is if on a 20A MCB the appliance can be over the rating of the socket! An appliance that draws 18 amps (that some fool has put a 16A plug on) Will sit there forever without ever knocking out the MCB! The socket is only rated at a duty of 16A not 18!!!
I'm not disputing what the OSG sais. I am saying I don't think it is very good practice.
Are you saying you could use a 63A MCB and a 16mm cable and can still put a 16A socket on the end because to quote you "it's only protecting the cable" and not the fact that some ****wit might try and plug in an oversized appliance!
I'm sorry if I am missing some logic here - I just don't quite understand why you can't see my point, regardless of what the OSG implies.
My point is if on a 20A MCB the appliance can be over the rating of the socket! An appliance that draws 18 amps (that some fool has put a 16A plug on) Will sit there forever without ever knocking out the MCB! The socket is only rated at a duty of 16A not 18!!!
I'm not disputing what the OSG sais. I am saying I don't think it is very good practice.
Are you saying you could use a 63A MCB and a 16mm cable and can still put a 16A socket on the end because to quote you "it's only protecting the cable" and not the fact that some ****wit might try and plug in an oversized appliance!
I'm sorry if I am missing some logic here - I just don't quite understand why you can't see my point, regardless of what the OSG implies.