If the appliance draws more than 16amp it shouldn't have a 16amp plug fitted.

How about if you use one of these? Never actually seen one, but I assume they're not fused?

ef821537-3e3b-49af-a576-6834905115cf.jpg

Edit: And what if you use that on the end of a 16A extension lead?
 
Well, thanks all for your posts, didnt really consider using a 16A breaker. In my understanding the MCB is there to protect the cable, as a circuit protective device.
And as long as the cable is adequately sized then no probs.

For the person who suggested rotary isolator and fixed wiring; they actually have 2 machines they want in use, however only one socket, only one machine will be used at a time. Otherwise this was my plan.

Final opinions now: 1 x 16A socket on 16A MCB or 20a???
 
didn't know you'd had a hip replacement, biff. :behead:
 
I agree with Biff go for the 16 amp type C MCB and state on your installation certificate that it is being used by a skilled or instructed person, or is marked up as a dedicated supply,
 