Love the smart meter just hanging there. 5 star installation 


or chase them in. then CU on a bespoke piece of board, spaced off wall with 4 bits of 1/2" long 20mm pvc conduit . then rear entry.Not strictly needed, but I would bring the board down the wall a bit to a more user friendly height. With trunking to hide cables.
Why do we fit RCDs for stuff buried in a wall less than 50mm deep if not to guard against things that aren't "normal use"??
Or use a stand off bracket rather than battening. Many manufacturers sell them.or chase them in. then CU on a bespoke piece of board, spaced off wall with 4 bits of 1/2" long 20mm pvc conduit . then rear entry.
As the board is going to be tight to the ceiling there won’t be room for trunking so may do the rear entry method. This is a photo of the old board being replaced.
And I generally space the board off a little with a couple of pieces of small batten the same height as the board to facilitate this.

I think you must do short course called part p etc ???Hey all,
I have just finished a rewire of a 1 bed house and just have the board left to install. I am a qualified sparky but now work as a project manger so haven’t carried out much domestic work in the last couple of years. I know that the requirements for installing consumer units has now changed and am wondering what are the requirements with regard to cable entries into the board. I have the cables all dropping down from the ceiling where the existing board and meter position is in the entrance hall. Any advice would be appreciated.
I assume the new board can be fitted to the existing wooden board behind also?
Why wouldn't it ?I assume the new board can be fitted to the existing wooden board behind also?
Have you consulted the seal fairy??Not sure thought I read something about it but I must be thinking of something else
Last point the existing tails are 16mm which will be fine as there will be little load being used. Anyone know how much roughly the DNO charge for coming out to pull the main fuse and back to reinstate supply after? It’s wpd here.