Hi, I need to install 2 separate underfloor heat mats both rated at 17A on individual 20A breakers. The heatmat controls are rated at 16A so I think it would have to go through a contactor right? I can install an enclosure in a cupboard for the contactors but would I have to use 2 x 1 pole contactors like this, or is a 2 pole contactor like this ok with 2 separate circuits running through it.

And just out of curiosity because I havent used contactors before, would it be possible to have the power to pull the relay in switched from a seperate circuit? So a supply from a control circuit, then 2 loads on there own circuits through 1 double pole contactor.

Thanks
 
i'd first speak to manufacturers ans see if that 16A rating has a bit of latitude. if using a contactor is necessary, then a 2 pole contactor is acceptable. ( label the contactor enclosure saying "2 circuits inside" or words to that effect). use whatever you like to energise the coil as long as it's installed safely.
 
Last edited:
Most contactors have two ratings inductive and resistive. So which rating do you use bearing in mind the load? You tell me and I’ll say if you’re right or wrong, then you’ll get help.
Do a bit of the work to get the answers, not unreasonable is it?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
2 17A Heat Mats Through Contactor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
atm-12,
Last reply from
dansk,
Replies
3
Views
1,315

Advert

Back
Top