A 32A mcb doesn't act as a current limiting device! and btw, 52A would take about 10 minutes to trip a B type mcb and likely won't trip at all until about 47A being drawn, so the Regs say anyway.
don't underestimate the general publics' ability to abuse sockets. was called out to an office some time ago as they said their sockets were tripping to find a fan heater connected next to everyone's desk.they had 8 2kW heaters connected drawing 66A and the mcb still hung on for a few minutes after re-setting! in the last Regs you could spur off a spur but that's been changed obviously.