Hellmooth
Thought it was maybe just the wonders of LED
250V is not high, it is correct. All UK substations are set to output 433/250V, regardless of the nominal voltage fairy stories you read about.
The faulty light switch is not related to the 'induced' voltage I must add!
Thanks for the input anyway Davesparks always appreciated, I will look into it further when I can be arsed..........
The reason I noticed it was because the LED bulb I was using was slightly dimmed when off lol
And yeah yeah that is the case, I was just putting the high voltage in with the rating of the switch being 250v, thought it may have caused a problem due to a poor switch, was just putting it out there.
Got a 2 way switch that gives 43 volts down one strapper when off, could this be an induced voltage, and if so why isn't it on the other strapper when it is off?
It's far more likely to be a capacitively coupled voltage rather than induced.
A phantom voltage such as this will not interfere with your dead testing due to the fact the circuit will be dead! Theoretically it could be an issue where multiple circuits are in close proximity and some remain energised, but I've yet to come across this being a problem for an MFT.
I'm gonna have to disagree with you there davesparks, but I know you'll put me right.
On a couple of occasions, my Megger mft (1730) would not conduct continuity tests, because it detected 'voltage'. Complete isolation of the installation, removed 'phantom, ghost, induced' etc voltage, and the MFT functioned correctly.
Have to say I didn't at the time due to my lack of expertise, but we all gain from our experiences. Now know what to think about in those circumstances.Did you try discharging the dead conductors by briefly connecting to earth? I doubt it would make a difference but am curious?