Got a 2 way switch that gives 43 volts down one strapper when off, could this be an induced voltage, and if so why isn't it on the other strapper when it is off?

Draw the circuit - think about the permutations. However it is wired, one strapper will always be at line potential. What is on the other(s) depends on which ends the PL & SL are connected.

Scheme 1) PL & SL to L1 & L2, all three terminals of both switches strapped
Light off: Strapper 1 at line volts, strapper 2 at or near neutral via SL & load, common wire could be either.
Light on: Both strappers and common at line voltage.

Scheme 2) PL to one com, SL from the other, L1 & L2 strapped
Light off: One strapper at line volts , other at or near neutral via SL & load
Light on: One strapper at line volts, other floating.

I.e. only in the last situation will one of the strappers be floating and likely to show a ghost voltage, unless the load is O/C in which case one strapper will be floating whenever the switches are in an off state.

A switch that physically sticks after being operated under load, has probably got badly pitted contacts. The tiny weld that forms at each operation, especially if the load has high inrush, can interlock the rough surfaces together. I had this on an MEM grid module, that would jam almost solid after switching about 500W of switch-start fluo, but worked normally off-load.

Rated voltages are nominal based on lifespan and safety and in practice the maximum usable voltage depends on the kind of load. A switch specced for 250V will probably switch 500, but with seriously reduced life and poor safety margin and a tendency to flash over with inductive loads. At very light load it might even handle 750.
 
It's far more likely to be a capacitively coupled voltage rather than induced.

A phantom voltage such as this will not interfere with your dead testing due to the fact the circuit will be dead! Theoretically it could be an issue where multiple circuits are in close proximity and some remain energised, but I've yet to come across this being a problem for an MFT.

I'm gonna have to disagree with you there davesparks, but I know you'll put me right.

On a couple of occasions, my Megger mft (1730) would not conduct continuity tests, because it detected 'voltage'. Complete isolation of the installation, removed 'phantom, ghost, induced' etc voltage, and the MFT functioned correctly.
 
I'm gonna have to disagree with you there davesparks, but I know you'll put me right.

On a couple of occasions, my Megger mft (1730) would not conduct continuity tests, because it detected 'voltage'. Complete isolation of the installation, removed 'phantom, ghost, induced' etc voltage, and the MFT functioned correctly.

As I said I've never yet had the problem, or at least can't remember it being a problem. That's not to say it can't happen, and from your experience obviously does happen.

Did you try discharging the dead conductors by briefly connecting to earth? I doubt it would make a difference but am curious?
 
Did you try discharging the dead conductors by briefly connecting to earth? I doubt it would make a difference but am curious?
Have to say I didn't at the time due to my lack of expertise, but we all gain from our experiences. Now know what to think about in those circumstances.
 
Last edited:

Reply to 2 way switch induced voltage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
594
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
842
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Is the following set up possible with a 3 Gang 2 Way Smart Wifi Switch set up (the black glass type touch ones) One of the 3 switches, switches...
Replies
2
Views
514
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
635

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock