This 100%Is this a construction site and are you an electrician.
Good morning sorry for the late replyIs this a construction site and are you an electrician.
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.
work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.
to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.
don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.
work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.
to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.
don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
I agree with you this new to meIt seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.
work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.
to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.
don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
You need to know the nature of the cabins, office, wc, welfare etc...
The most they will have is a couple of 2kw heaters, lighting and mostly low load appliances apart from a kettle or a few kettles. 16.0 is likely to be overkill.
Thanks againThe cabins do not fall under Section 704 so TN-C-S can be used however the supplier may not have provided an earth so it may be TT anyway.
The cabins do not fall under Section 704 so TN-C-S can be used however the supplier may not have provided an earth so it may be TT anyway.