Hi everyone need help pls

I need to power 2 x portable work cabin

The meter people came today installed new supply with one meter 25 meters away from the 2 cabin

Each cabin have 3 heaters sockets lights

My question is what size Swa cable can I use

Cable length 35 meters from meter box
 
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.

work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.

to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.

don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
 
It's not really any different from any other circuit design, you need to arrive at what current each unit will draw after some diversity (as the heaters will presumably be thermostatically controlled), then consider how cable is run, and volt drop and fault protection.

(I would suspect these will not be allowed to be connected to TN earthing but I haven't read section 7 and checked. Certainly the mobile/transportable units section would prohibit it, but I'm not familiar with the Construction Sites section)
 
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.

work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.

to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.

don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.

Thank you
Will have to wait and see what the big electricians going to advice me

For example if they say use 2 x 16mm swa to each one this mean I need second electrical box next to the meter with small fusebox to glan the 2x Swa .

I'm confused
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.

work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.

to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.

don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
 
It seemed to be a very simple question and because of that I suspect that many people wondered if you were undertaking something outside of your knowledge base And experience.

work cabins in my experience tend to have an appliance inlet on the side and this can vary between 16A and 63A generally.

to be on the cautious side, I would assume the rating of the inlet is the maximum demand.
pick your cable type, probably swa? Have a look at the cable rating tables in the back of the book and post your results here for a double check.

don’t forget to consider earthing type and arrangements or possibly the need for an rcd or 2 of differing types maybe.
I agree with you this new to me

To be honest I don't want to do it ,
But if I do it I can have the 14 house later which I love to do empty house rewire that's what I been doing for the last 8 years
 
You need to know the nature of the cabins, office, wc, welfare etc...
The most they will have is a couple of 2kw heaters, lighting and mostly low load appliances apart from a kettle or a few kettles. 16.0 is likely to be overkill.
 
16mm swa is way to much but if I decided to use it the system is tnc-s

Reading few minutes ago say cant use the earthing if it Tn system ,I'm confused pls pls
Does this mean I need to install a Earth rod
 
The cabins do not fall under Section 704 so TN-C-S can be used however the supplier may not have provided an earth so it may be TT anyway.

I realise it's rarely complied with but would the cabins themselves they not fall under Section 717 wherever they are?
"Unless these installations are under continuous supervision by a skilled or instructed person and the effectiveness of the means of earth has been confirmed prior to connection, TN-C-S systems are prohibited."
 
I agree that a cabin used as a canteen does not fall under 704 Construction Sites.

I also agree that under Section 717, Mobile Or Transportable Units, a PME supply may used, if the installation is continuously under the supervision of a skilled or instructed person. It could easily be argued that, as the cabin is associated with a construction site, it is therefore under such supervision.
 
We going to far on this job I need experience electrician to say run the cable put another rod if I have to and get powered
Even if I have to pay him for his correct advice I don't want see section numbers ,

If it can't be done then I just going to pull out

Im sure someone will come and give the correct way
 
I dread to think what the wiring in the 14 houses would look.like if this is such a tricky concept for him to get his head round....

You don't want to see section numbers?!! So what your actually saying is you can't be bothered to educate yourself on this, you just want someone else to do the thinking for you and give you free advise?
Hi everyone I don't want to you to understand wrong off course I want to follow and respect the Bs7671 all I'm asking is help from the boys who's doing this all day long
I all ready put my hands up and said I'm domestic never worked in this field ,if I knew all this I wouldn't ask for help

House rewire is easy for me I do it all day long

We all have to respect each other and work forward
 
Thank you
Will have to wait and see what the big electricians going to advice me

For example if they say use 2 x 16mm swa to each one this mean I need second electrical box next to the meter with small fusebox to glan the 2x Swa .

I'm confused

That would be the easiest way, enclosed in some sort of weatherproof structure which the builders will probably be happy to make. Then run appropriate circuit to each cabin.
 
I can't see how section 717 can't apply it lists transportable as containers and cabins and lists welfare units. They are designed to be transported.

If it's pme TT it. If it's a 32 amp plug or under it needs a rcd anyway.

Prysmian do a free cable app that may help start you off with the right size cable.
 
I can't see how section 717 can't apply it lists transportable as containers and cabins and lists welfare units. They are designed to be transported.
I don't want to start a huge diversion on this topic but this does seem to be an area where different sparks have different interpretations both as to what's in scope, and what constitutes continuous supervision by skilled or instructed people. If you look back at previous threads it's been discussed before on this forum and the iet forum.

I have some sympathy for the argument that the more structures move, the more relevant section 717 is. For example an outside broadcast unit (in a past life I drove one and was the resident engineer) could move every day and be connected to a different supply daily. That is a good example of something being under continuous supervision too. Which is handy as banging an earth rod in at every venue for the antiques roadshow isn't really practical!

Even if this section was in scope, it's been pointed out there is likely to be someone skilled supervising things on a construction site. So PME would be allowed.
 

Reply to 2 x portable work cabin in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top