During Periodic Inspection and Testing, prospective fault current has been tested at the main distribution board (Main DB) using a single-phase test instrument.

The supply and installation form part of a 400 V three-phase TN-C-S system. The value of Zₛ (earth fault loop impedance) for this installation is 0.05 Ω.

Information about the protective devices installed at the remote distribution boards (DBs) is as follows:

Main DB: 3 phases, 10 kA
DB1: 3 phases, 7.5 kA
DB2: 3 phases, 7.5 kA
DB3: 1 phase, 7.5 kA
DB4: 1 phase, 6 kA

At which points in the installation must further testing be carried out?

a) DB1 and DB2
b) DB3 and DB4
c) DB1, DB2 and DB3
d) DB1, DB2 and DB4
 
The key here is calculating your pfc for the three phase and single phase because two boards are single phase and the other two three phase. Then as in #6 which ones then need checking.
 
Upvote 0
The key here is calculating your pfc for the three phase and single phase because two boards are single phase and the other two three phase. Then as in #6 which ones then need checking.



Further testing should be carried out at DB1, DB2, and DB4 to confirm that the PFC at these points does not exceed the breaking capacities of their respective protective devices is to hid correct ?
 
Upvote 0
You can work out what the PFC should be when tested single phase given the information.

You can then convert that to 3 Phase PFC.

With that information think about which DB protective devices short circuit breaking capacity might need checking.
the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?
 
Upvote 0
the correct answer would include the boards with the lowest breaker ratings, especially single-phase ones, where the PFC formula gives a different result ?
This is a periodic Inspection and test, when you test on a Periodic a test result might give you reasons to perform further tests and this is what the question is probing.

Think about PFC and what it cannot be at points further from the origin?

Given the above info why the single phase ones when we know the maximum single phase PFC at the origin?

Why the 3 phase ones?
 
Upvote 0
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Right business

Thread Information

Title
2391-52 help please
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Kaya12,
Last reply from
westward10,
Replies
10
Views
182

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top