L
Lucas123
Is there any reg or scenario where it is acceptable to have 3 line conductors in the same 32A 60898 protective conductor ?
Still ascertaining wheter two of which are a ring final but if they are is there some way that is allowed ? A RFC and a another Fused spur circuit in the same protective device
im sure i read it somewhere but cant find it anywhere in the regs ?
Yes, it effectivly makes the conductors all part of the same circuit.
Have a look at appendix 15.
You say 3 conductors in a 32 amp device I take it that there is 3 2.5mm cables on a 32 breaker in other words I take it is a ring main and someone has spurred of a circuit like they would out in the field
as long as the radial has no more than 1 socket outlet ( single or twin) it need not be fused down and is OK. it's just a spur off the RFC at the CU. ( assuming that the other cables are a RFC. you'll have to test end/end to see)
Agreed its in the regs in the back and is acceptable, the thing that confuses me is my firm on testing encourage us to record more than 2 conductors in one mcb as mechanically unsound for some reason??? (prob my firm wont mention name but they are a shower of... and one of the big ones)
Some of the older 3871 mcb's had a clamp plate terminal which was hopeless with more than two conductors...perhaps it stems from that.