Hi,

I am installing a new distribution board. It is supplying 2 compressors, 2 Air dryers and a 13A socket.
Is it ok to use a 3 pole isolator as a means of isolation or do I need to disconnect the neutral also?

:confused:!!
 
we only have tn-c-s here so the neutral isn't switched

if you need to break all lives for TT -the isolator may edit: break neutral last and make first!


had it wrong way round
 
Last edited by a moderator:
Is there any benefits to using a 4-pole device??? Is there any situation where you are not aloud to use a 4-pole device???
 
From what i gather you should use a 4 pole in all systems that are not TN, TN-C and TN-C-S.
I am open to correction on this!
 
In TNC systems the PEN conductor shall not incorparate a means of switching or isolation. In TNS the same, and PROVISION NEED NOT be made for isolation of the neutral conductor EXCEPT required for High voltage discharge lighting, water heaters and suchlike. Thats why there is a DP switch on an immersion heater.
 
From an inspectors point of view
3 pole - strip down the unit to get to the neutral. disconnect the neutral link (if they are fitted) reassemble the unit
4 pole - done in seconds
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 or 4 pole Isolator?????
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
gerard,
Last reply from
controlman,
Replies
7
Views
12,297

Advert

Back
Top