3 x 20 Amp supplies would be ok. Certainly not 3 x 63
I thought three phase was supposed to be 120 degrees out of phase with each other. So the neutral gets a rest. 180amps.... does not work like that.sorry must disagree, as the op states he wants 3 x 63A Single phase supplies. Fully loaded you can have a current of 180 Amps flowing down the neutral. 3 phase machines are different, because any unbalanced currents just flow down the neutral.
SQRT I²A + I²B + I²C - (IA x IB) - (IB x IC) - (IC x IA)
Now look you lot lol, imagine the Switch fuse or Isolator the OP mentioned was a distribution board yes? and you run 3 single phase supplies from the Distribution board to seperate switch fuses or Isolators? would you need to rip out the main neutral and install one 3 times larger than the phase cables? think about it.
You can have inductive load, capactive loads, and resitive loads each all on one phase each. Which will pull well in excess 63 Amps fully loaded.
It would be absolutely fine to have Three 63A Single phase supplies (one on each phase) run from a 63A Three Phase supply as the Neutral currents would cancel out (unless you had harmonics etc)...amazed at the ignorance of basic electrical theory on here.
Hopw else do you think something like this would work... Rubber Box - Type 270 Power Distro Box
Never seen an armoured cable with 3 cores which are 10mm2 and one which is 30mm2 LMAO