L
Lucien Nunes
Or get yerself one of these. Ex power station control room mid 1960s., changed one duff valve and a leaky capacitor and up it came within 0.01 Hz of my bench FG. Trouble is, if you want to wake up in the morning knowing whether your clock is running at the right speed, you've got to be able to sleep through the funny little noises it makes - the pointer is driven by a servomotor so it whirrs and hums all the time as the frequency changes. You also need a strong wall to put it on! Note the red marks on the dial - load shed is at 48.50Hz and island mode on the 132kV at 47.6.
Flicking back through the thread, the reference to the current being wrong 'because the OP hadn't built in a factor of sqrt(3)' - he had, you just didn't see him do it. He used the line current but the L-N voltage, which includes the division by sqrt(3). Saves space on the envelope.