H

Hereforhelp

Hi all,



I’ve been asked to run a cable for a 3 phase DC motor. Not having much experience with motors would you work out cable sizing the same?



In the picture attached are the details I have received.



Any help would be great 
 

Attachments

  • DC207B96-E3DA-467B-B734-8EEB05482146.jpeg
    DC207B96-E3DA-467B-B734-8EEB05482146.jpeg
    131.5 KB · Views: 131
Last edited by a moderator:
As far as I know, there is no such thing as a 3 phase dc motor.
from the nameplate, i would guess that it is a servomotor.
there are special types of cables used to connect them to the servo drive.
 
Can someone tell why a DC motor would have a frequency of 50Hz on the rating plate which clearly shows in the OP's picture

I assume that is a very large motor with a nominal weight of just under 5.6 Tonnes
 
I suspect either soneone is winding the OP up, or he is winding us up.

Until he comes back we won't know though.
 
motor calcsPNG.PNG



4mm2 cable method C , min depending on the length of the circuit. Don't forget volt drop & startup current for choice of mcb. Please do your own check calculation to clarify the above.
 

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Thread statistics

Created
Hereforhelp,
Last reply from
davesparks,
Replies
11
Views
2,271
Back
Top