Hi all,



I’ve been asked to run a cable for a 3 phase DC motor. Not having much experience with motors would you work out cable sizing the same?



In the picture attached are the details I have received.



Any help would be great 
 

Attachments

  • DC207B96-E3DA-467B-B734-8EEB05482146.jpeg
    DC207B96-E3DA-467B-B734-8EEB05482146.jpeg
    131.5 KB · Views: 131
Last edited by a moderator:
As far as I know, there is no such thing as a 3 phase dc motor.
from the nameplate, i would guess that it is a servomotor.
there are special types of cables used to connect them to the servo drive.
 
Can someone tell why a DC motor would have a frequency of 50Hz on the rating plate which clearly shows in the OP's picture

I assume that is a very large motor with a nominal weight of just under 5.6 Tonnes
 
I suspect either soneone is winding the OP up, or he is winding us up.

Until he comes back we won't know though.
 
motor calcsPNG.PNG



4mm2 cable method C , min depending on the length of the circuit. Don't forget volt drop & startup current for choice of mcb. Please do your own check calculation to clarify the above.
 