See post #42. ARE YOU STILL FINDING THIS HARD TO GRASP?
so you don't think 10mm is enough to supply 10kw load? thats what I meant by "doesnt matter what the load is" what ever happens the load is supplied sufficiently, more than. Phase 1, 10mm is going to be supplying the steam gen. Phase 2 and 3, un needed. ARE PEOPLE STILL FINDING THIS HARD TO GRASP

Use 3 cores of the 10mm2 armoured and coil the 4th up as a spare, the third core can be the CPC, then just connect to a single phase breaker, the other end I assume is a rotary isolator? if so just connect the live and neutral through it and connect to the single phase kit, simples
To be fair MDJ wouldn't you connect the spare down to earth?
So long as the spare core is totally isolated both ends, shouldn't be any problem at all. You could i suppose connect the spare core to earth at the DB end, maybe even at the local isolator as well, if sufficient earth terminals are available, but it's not really necessary!!