Search the forum,
Discuss 3 phase question in the UK Electrical Forum area at ElectriciansForums.net
hi guys
can someone explain to me this
a 3 phase supply to bungalow ok
one phase to house ok live
neutral& earth in henley blocks in meter box
neutral to 3phase meter from henley block
we have l1 l2 l3 lives to tpn 100amp switch fuse ( no neutral )
earth connection via earth block
from there we have a 16mm 4 core swa ( black ,red ,blue & yellow)
black --l1 fuse
red-- l2 fuse
blue--l3 fuse
yellow -- earth to henley block
thus feeds a 3phase board in workshop
No neutral to it.
1..???? is why is there no neutral to it
its not connected to earth
swa at cu is bonded at the armourings back to earth connection in board
and not at tpn ( discrimination)
2..??? why does all the 3phase equipment still work without a neutral
i am having to update a single phase cu to a 6 way to accomodate a solar pv 9.9kw system
luckily its got a 10.mm feed to it.
thanks
jon
hi guys
black --l1 fuse
red-- l2 fuse
blue--l3 fuse
No neutral to it.
thanks
jon
ballanced loads mate...motors.
however...just looking at what you have decribed as L1 L2 & L3...
since when has L1 been black?
it should be
red=L1
Yellow=L2
Blue=L3
so something not right here...unless its just a case of someone not following the colours...or a phase reversal at the intake...
have you done a phase rotation on it?
Looks like the 3 phase supply was installed just for 3 phase machines/motors ,( no neutral required on 3 phase motors )
The 4 core swa is not wired correctly , but I suspect it tallies at both ends also,,
theres a sub feed from house cu to a workshop single phase to power lights sockets
ta
jon
- - - Updated - - -
ta
jon
It looks like there was an original single phase supply , and then had 3 phase installed at a latter date, you see this a lot ,,,
The mystery solved ........
and yes most definately .......
Seems somebody went about the initial job in a strange sort of way....
- - - Updated - - -
And further intrigue to the plot ........
OK.
so i distinctly remember asking if a phase rotation had been carried out here
as
it is:
black --l1 fuse
red-- l2 fuse
blue--l3 fuse
and theres no identification rings then its a contravention of 514.3
saturn's got all the rings: jupiter's got all the moons:and i ate all the pies. so there.
looks like a diy job to me the 3phase
BUT i wont be using the 3ph db
i shall be using the single phase board i will be making it a 6 way instead if the 3 way installed via 10 mm feed
1x 32 ring
1 x 6 amp lights
1 x 20amp to paint booth
3 x 16amps for pv
It seems 3ph PV system is being connected to 3x16A mcb's in a 1ph DB, which is not at the origin of the installation, thus downstream of some protective devices, thus negating the function of said protective devices, with regard to ADS and relying upon the PV inverter to undertake the disconnection.
What else do you want?
Do you think it's OK to skew the supply by 48A of PV? infeeeding to a single phase.
Will the DNO OK this, will it be OK, is it OK, what more.
I despair, I really do.
I really will not comment any more on this thread, so don't even bother to try to get me to.
Reply to 3 phase question in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
