The moment someone mentions a 400a MCCB repeatedly tripping I get worried.
With a 400A MCCB, if it was damp in an enclosure or on equipment there would be obvious blast damage. Similarly if the cable is damaged the fault will cause a drop in the insulation resistance which as Tel has pointed out you should test for. If this comes back clear I would start by checking the normal / abnormal running current of the equipment and the possibility of transient overloads.
The more information you can give the better the answer. Otherwise you’ll get the board’s speciality, wild guesses.
this is more like it.........there is no obvious blast damage........there is no access to the outer sheath of the cable, the cable is buried.........the previous installation was to NEC standards now converted to BS, meaning the yanks installed the main feeder cables using swa but never glanded to the panel as this not a requirement in the nec code.........Done an insulation resistance test and a continuity test........between L1 & L3 to earth the reading we're gettin is around 280 ohms........