The moment someone mentions a 400a MCCB repeatedly tripping I get worried.

With a 400A MCCB, if it was damp in an enclosure or on equipment there would be obvious blast damage. Similarly if the cable is damaged the fault will cause a drop in the insulation resistance which as Tel has pointed out you should test for. If this comes back clear I would start by checking the normal / abnormal running current of the equipment and the possibility of transient overloads.

The more information you can give the better the answer. Otherwise you’ll get the board’s speciality, wild guesses.

this is more like it.........there is no obvious blast damage........there is no access to the outer sheath of the cable, the cable is buried.........the previous installation was to NEC standards now converted to BS, meaning the yanks installed the main feeder cables using swa but never glanded to the panel as this not a requirement in the nec code.........Done an insulation resistance test and a continuity test........between L1 & L3 to earth the reading we're gettin is around 280 ohms........
 
Sorry to say this, looks like you've got some digging to do.

Back in a minute. Got a calculation kicking about somewhere that may help finding where to dig.
 
Can you fill in the values? They're going to have to be faily accurate.
cablefault.jpg
 
this is more like it.........there is no obvious blast damage........there is no access to the outer sheath of the cable, the cable is buried.........the previous installation was to NEC standards now converted to BS, meaning the yanks installed the main feeder cables using swa but never glanded to the panel as this not a requirement in the nec code.........Done an insulation resistance test and a continuity test........between L1 & L3 to earth the reading we're gettin is around 280 ohms........


I think you'll find that glanding of SWA cables IS a requirement under NFPA 70 (NEC electrical codes) But like the UK, there is always a rouge element!! lol!!

You won't need a sheath test with IR readings like that. As Tony stated looks like you or someone else is in for some digging!!
 
Can you fill in the values? They're going to have to be faily accurate.
cablefault.jpg

And that will only work if you accurately know the route taken by this cable!! Otherwise it's all down to your thumper and looking for the smoke!! lol!!
 
Tony this sounds promising, can you provide me with this calculation. I do suspect that this cable has been slightly damaged during a trench dig which has been backfilled ,and moisture has took an affect.
 
Original poster lol. I have came accross similar situations here. As long as its not feeding the DFAC then you've got all night to get it sorted lol. Have they peeled the armour like a bananna like they have here?
 
stripped it back cut the strands off put in a duct 2 feet away from the sdp.......im goanna have to smash the duct and put a split bolt on the armoured sheath..........i reckon this will clarify if the cables damaged
 
its been like this for a week now ........new construction been here to wire a few tin cans.......military dug a trench......then all the problems started lol
 
Problem is we knock someone back , they get a red face and respond in an over defensive manner ,
pat him on the back there there go and do a resit!
 