Hi,

been asked to wire 3 x 1.5kw heaters in offices in an old warehouse.

2.5mm radial - 20amp rcbo with 20amp DP switch with flex outlets

That sound about right?
 
Sounds near the knuckle, whats the history?

Any history of tripping, visual signs of cable damage.
The old heater that’s in just now is a 3kw on a 16amp breaker but has gave up and they want it replaced - but have also asked for another 2 added to this. There’s only 1 way left on the distribution board that’s the problem I have
 
The old heater that’s in just now is a 3kw on a 16amp breaker but has gave up and they want it replaced - but have also asked for another 2 added to this. There’s only 1 way left on the distribution board that’s the problem I have
Put a larger CU in
 
Sounds near the knuckle, whats the history?

Any history of tripping, visual signs of cable damage.

Re
The old heater that’s in just now is a 3kw on a 16amp breaker but has gave up and they want it replaced - but have also asked for another 2 added to this. There’s only 1 way left on the distribution board that’s the problem I have
Ah, new heaters on old existing circuit.

Installation method? It'd take a lot to derate 2.5 down to less that 20A mind.

19.6A load, then cycling would most likely be fine.

Any chance of throwing a return leg in and making it a ring?
 
Re
Ah, new heaters on old existing circuit.

Installation method? It'd take a lot to derate 2.5 down to less that 20A mind.

19.6A load, then cycling would most likely be fine.

Any chance of throwing a return leg in and making it a ring?
Would be very awkward but could make it a ring, the cable is run above ceiling tiles but runs through insulation which is a problem
 
You could demolish the warehouse and relocate the business to warmer climes and have no need for the heater.

There's a lot you could do but I expect, like me, you have a customer on a budget and are trying to give them something that will work, is safe and is compliant.

What you are suggesting appears to fit those criteria.
 
Would be very awkward but could make it a ring, the cable is run above ceiling tiles but runs through insulation which is a problem
If that's the case then a thorough assessment of the installation method is needed to ascertain the derating required.

A return leg may be the best route, gives more wiggle room and peace of mind.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
3 x 1.5kw heaters on one circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
Mabro22,
Last reply from
Wilko,
Replies
27
Views
6,276

Advert

Back
Top