Pete it's a fraction under 20 amps, not 30.
Discuss 3 x 1.5kw heaters on one circuit in the UK Electrical Forum area at ElectriciansForums.net
Pete it's a fraction under 20 amps, not 30.
Some things are not as difficult as you think they are going to be.Would be very awkward but could make it a ring, the cable is run above ceiling tiles but runs through insulation which is a problem
If that's the case then a thorough assessment of the installation method is needed to ascertain the derating required.Would be very awkward but could make it a ring, the cable is run above ceiling tiles but runs through insulation which is a problem
Ignore the question my badWhat Voltage are you using?
That’s what I was thinkingYou could demolish the warehouse and relocate the business to warmer climes and have no need for the heater.
There's a lot you could do but I expect, like me, you have a customer on a budget and are trying to give them something that will work, is safe and is compliant.
What you are suggesting appears to fit those criteria.
The invoice for the design consultation will follow shortly.That’s what I was thinking
But I think I’ll just go for 4mm radial with 13amp switched fused Spurs at each heater