Can someone confirm longest legth for a ring main using 4mm singles P,N & E that can be run without exceeding max voltage drop or Ze ?
I have a length in mind, but don't wish to appear a ----, so will await some answers and then nod my head in agreement :)
Thanks in advance
for 105m i get 1.36Ω for Zs...which is OVER the max. of 1.2Ω (1.15Ω for 17th). using a TN-C-S supply and a 32A type B 60898.
therefore the length of the circuit would need to be reduced to bring it into compliance with the max Zs. (would do the math but have had one of those days :()
Max circuit length to comply with both voltage drop and Zs is: 88.6m (83.4m for 17th)
for 105m i get 1.36Ω for Zs...which is under the max. of 1.5Ω. using a TN-C-S supply and a 32A type B 60898.
yep 1.36 for Zs. Tabulated value of 1.5 (1.44 in 17th edition)
so max value that you be allowed to read on the circuit is 1.12 ohms, and so the 1.36 would not comply. thats why we dont design to the maximum!
good call Shakey, my bad. took value out of wee brown amicus book; assumed it was the adjusted value. know what they say about assumptions... :(
edited post to avoid any confusion, cheers.
Reply to 32A ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
  • Locked
5K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Good morning I wonder if I could have some confirmation in regards to a radial circuit. I have been showing apprentices different methods if...