Can someone confirm longest legth for a ring main using 4mm singles P,N & E that can be run without exceeding max voltage drop or Ze ?

I have a length in mind, but don't wish to appear a ----, so will await some answers and then nod my head in agreement :)

Thanks in advance
 
for 105m i get 1.36Ω for Zs...which is OVER the max. of 1.2Ω (1.15Ω for 17th). using a TN-C-S supply and a 32A type B 60898.

therefore the length of the circuit would need to be reduced to bring it into compliance with the max Zs. (would do the math but have had one of those days :()


Max circuit length to comply with both voltage drop and Zs is: 88.6m (83.4m for 17th)
 
Last edited by a moderator:
for 105m i get 1.36Ω for Zs...which is under the max. of 1.5Ω. using a TN-C-S supply and a 32A type B 60898.

yep 1.36 for Zs. Tabulated value of 1.5 (1.44 in 17th edition)

so max value that you be allowed to read on the circuit is 1.12 ohms, and so the 1.36 would not comply. thats why we dont design to the maximum!
 
good call Shakey, my bad. took value out of wee brown amicus book; assumed it was the adjusted value. know what they say about assumptions... :(

edited post to avoid any confusion, cheers.
 
Last edited by a moderator:

Reply to 32A ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
735
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Good morning I wonder if I could have some confirmation in regards to a radial circuit. I have been showing apprentices different methods if...
Replies
27
Views
3K
Hi, I'm an industrial spark and taking my 2391 next week (wish me luck, I need it). I decided to get a bit of practice and started an inspection...
Replies
43
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock