I understand this Pete but a motor that only draws 3A on start up doesn't need to be connected to a star delta starter to reduce starting current does it? without seeing the rating plate it's obviously small motor
What does the information relate to on the starting procedure? there must be some information regarding this. I f it's a small motor then we must ask the question why is star delta mentioned, what has happened to the rating plate?
No not blown it out but it runs fine when connected to dol started with links in motor 3 wire.
It seems like losing a phase / low voltage high current???
If you were trying to start this motor via a star delta starter, there should be no links in at the motor terminal block, you would need 6 six wires from the starter to the motor.
This is my point, the OP has gathered components off a shelf and assembled to test either that the star delta starter is operational or that the motor is ok, but not every motor can be connected to a star delta motor as you know.
Never said was a star delta motor. It's just 2 items out of stores we were checking that are ok.
It really has to be the delta contactor if running fine in star, proves windings are ok, loosing a phase when delta contactor comes in.
h
It
I would like to see a photo of the OPs connections if running fine in star, proves windings are ok, loosing a phase when delta contactor comes in.
Can the OP provide pictures of how he has connected the motor and the starter? this may help us to get to the answer, after all it may be just a simple mistake in the final connections.
Could a set of the windings be connected to the same phase e.g. U1 and U2
Edit, Andy 1960 already mentioned this.
I would double check the wiring as the motor could be single phasing when it goes into delta ( same phase across both end of the one winding)
It shouldn't take 5 seconds to trip. though.
Delta contactor problem.
....then again, if there are motor links, who knows? Someone playing about with something they shouldn't be springs to mind.
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.
This statement is anomalous if you consider what you would measure with a voltmeter between the terminals of the Star and the Delta diagram in my post #15.
eg for STAR - One would measure 230V from each 1 to any 2 but between any 2s would measure zero Volts.
eg for DELTA - One would measure 415V between any pair of 1s or any pair of 2s.
Between U1 - W2, V1-U2 or W1-V2 one would measure zero Volts.
Reply to 3ph star delta starter motor drawing high amps in the Electricians' Talk area at ElectriciansForums.net
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
5K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...