Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.


Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
Does the motor have a load connected to it?
Also check insulation resistance tests of the windings and continuity of windings.
 
  • Agree
Reactions: 1 person
Is this a recent problem on an existing motor or an issue on a new install.
PS. No such thing as a star/delta motor.
 
  • Agree
Reactions: Pete999
can you offload it onto a coworker? take time off work and hope its fixed when you get back?
 
You need to clarify your opening post it is somewhat confusing.
 
Does the motor have a load connected to it?
Also check insulation resistance tests of the windings and continuity of windings.
No load just on bench. Insulation is acceptable. In runs fine in start so presume windings are fine.
 
how long has it been in stores? corrosion ? have you taken it apart or blown pressurised air through it?
 
how long has it been in stores? corrosion ? have you taken it apart or blown pressurised air through it?
No not blown it out but it runs fine when connected to dol started with links in motor 3 wire.
It seems like losing a phase / low voltage high current???
 
could be a few things, im no expert on motorwindings but when they lose balance tends to be when things go pete tong, was there a reason it was stored away no longer used or was it working last time it was tested?
 
I would double check the wiring as the motor could be single phasing when it goes into delta ( same phase across both end of the one winding)
 
main-qimg-e11f98040c68f35a3d1cd631a1976404-c
 
  • Like
Reactions: Wilko
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.
When you say the Starter runs OK with no Motor connected, are you saying the Starter operates as it should? and what do you mean by single speed?
If the Motor is starting, and connecting the Motor's winding in a Star configuration, but trips when it changes into a delta mode, then it sounds like you have either a faulty Motor, of you have it wired up incorrectly.

Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.


Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
  • Like
Reactions: Wilko
No not blown it out but it runs fine when connected to dol started with links in motor 3 wire.
It seems like losing a phase / low voltage high current???

Why do you need to start it via star delta if you are able to start it DOL, how big is the motor and are the windings rated 415/690 or there abouts?

How are you connecting the links when starting DOL I presume star as you say it starts fine when connected up to the star delta.

My bets on delta contactor in starter... although I can't understand from your original post if you've checked this?
 
Why do you need to start it via star delta if you are able to start it DOL, how big is the motor and are the windings rated 415/690 or there abouts?

How are you connecting the links when starting DOL I presume star as you say it starts fine when connected up to the star delta.

My bets on delta contactor in starter... although I can't understand from your original post if you've checked this?
https://www.quora.com/Why-is-star-delta-starter-preferred-with-an-induction-motor
 
Last edited:
I understand this Pete but a motor that only draws 3A on start up doesn't need to be connected to a star delta starter to reduce starting current does it? without seeing the rating plate it's obviously small motor
What does the information relate to on the starting procedure? there must be some information regarding this. I f it's a small motor then we must ask the question why is star delta mentioned, what has happened to the rating plate?
 
No not blown it out but it runs fine when connected to dol started with links in motor 3 wire.
It seems like losing a phase / low voltage high current???
If you were trying to start this motor via a star delta starter, there should be no links in at the motor terminal block, you would need 6 six wires from the starter to the motor.
 
  • Agree
Reactions: ipf
What does the information relate to on the starting procedure? there must be some information regarding this. I f it's a small motor then we must ask the question why is star delta mentioned, what has happened to the rating plate?

This is my point, the OP has gathered components off a shelf and assembled to test either that the star delta starter is operational or that the motor is ok, but not every motor can be connected to a star delta motor as you know.

Never said was a star delta motor. It's just 2 items out of stores we were checking that are ok.
 
  • Agree
Reactions: Simon-0116
It really has to be the delta contactor if running fine in star, proves windings are ok, loosing a phase when delta contactor comes in.
 
  • Agree
Reactions: Simon-0116
Never said was a star delta motor. It's just 2 items out of stores we were checking that are ok.
This is my point, the OP has gathered components off a shelf and assembled to test either that the star delta starter is operational or that the motor is ok, but not every motor can be connected to a star delta motor as you know.
h
It
I would like to see a photo of the OPs connections if running fine in star, proves windings are ok, loosing a phase when delta contactor comes in.
It really has to be the delta contactor if running fine in star, proves windings are ok, loosing a phase when delta contactor comes in.
Can the OP provide pictures of how he has connected the motor and the starter? this may help us to get to the answer, after all it may be just a simple mistake in the final connections.
 
Please ignore my post #22 which has a gross wiring error in the diagram - can you spot it?
 
Could a set of the windings be connected to the same phase e.g. U1 and U2

Edit, Andy 1960 already mentioned this.
 
Last edited:
I would double check the wiring as the motor could be single phasing when it goes into delta ( same phase across both end of the one winding)
It shouldn't take 5 seconds to trip. though.
Delta contactor problem.
....then again, if there are motor links, who knows? Someone playing about with something they shouldn't be springs to mind.
 
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.

This statement is anomalous if you consider what you would measure with a voltmeter between the terminals of the Star and the Delta diagram in my post #15.

eg for STAR - One would measure 230V from each 1 to any 2 but between any 2s would measure zero Volts.

eg for DELTA - One would measure 415V between any pair of 1s or any pair of 2s.
Between U1 - W2, V1-U2 or W1-V2 one would measure zero Volts.
 
Last edited:
  • Like
Reactions: static zap
Have you checked delta contactor? Could be a phase down
 
You have removed the links when you connected the motor to the star delta contactor?
 
Hi yes we was testing separate items out of stores. So not knowing conditions of either item.
Motor was original connected to dol and ran fine.
Obliviosly links were took out to connect to 6 wire star delta.
Thinking must be delta contactor problem.
But just curious now as someone mentioned not all 6 wire motors will run on. Motor reminders confirm motor will run in either.
Anyway items been put back on shelf for another rainy day tidy up.
Thanks for everyone's help.
 
Hi yes we was testing separate items out of stores. So not knowing conditions of either item.
Motor was original connected to dol and ran fine.
Obliviosly links were took out to connect to 6 wire star delta.
Thinking must be delta contactor problem.
But just curious now as someone mentioned not all 6 wire motors will run on. Motor reminders confirm motor will run in either.
Anyway items been put back on shelf for another rainy day tidy up.
Thanks for everyone's help.
Three phase squirrel cage motors will have 6 ends at the terminal block, it's how they are connected that determines how they start and run.
 
My money is it not being wired correctly.

When going into delta it's ending up running on 2 phases. Seen it dozens of times with people who don't have much experience with them.

If it runs fine in star then the motor is fine.
 
  • Like
Reactions: static zap
This is exactly the mistake I presume it to be, should have read the comments before responding.
Using the Erroneous diagram , with K3 closed .
Are we looking at a form of symmetry forcing L1 and L3
into a tussle , and possible some circulating currents in the V1 & V2 contacts of K3 ?
Not Pretty !
(Spotted quite a few suspect /tweaked diagrams -Googling!)
 
  • Winner
Reactions: marconi
As static zap said - The erroneous diagram in delta mode connects the U and W windings in parallel across L1 and L3 and shorts the V winding (and connects it to L2 only at one end but no current is drawn from L2). Acting as a three similar winding transformer and Lenz's Law, the alternating magnetic fluxes around each winding must be equal in magnitude and together sum to zero. Thus the currents in each winding are the same in magnitude. The OP sort of told us this in his first post - 'taking 38A on all' - the currents being 120 electrical degrees apart).
 
Last edited:
  • Like
Reactions: Rocboni

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3ph star delta starter motor drawing high amps
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
Simon-0116,
Last reply from
marconi,
Replies
37
Views
10,163

Advert