Discuss 559.5.1 18th Ed. p219 Luminaire fixed connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
John-
Hi
559.5.1. My question is that for any luminare in the UK must be complaint to one of the methods (BS standards) listed in the list, or else we would not be compliment fitting and connecting to? Is that correct?
So if the fitting is not supplied with any details in relation to the points listed on p219, technically we cannot fit it unless we of course put something inside of it that does comply?
John
559.5.1 Connection to the fixed wiring
At each fixed lighting point one of the following shall be used for the termination of the wiring system:
(i) A ceiling rose complying with BS 67
(ii) A luminaire supporting coupler (LSC) complying with BS 6972 or BS 7001
(iii) A batten lampholder or a pendant set complying with BS EN 60598
(iv) A luminaire complying with BS EN 60598
(v) A suitable socket-outlet complying with BS 1363-2, BS 546 or BS EN 60309-2
(vi) A plug-in lighting distribution unit complying with BS 5733
(vii) A connection unit complying with BS 1363-4
(viii) Appropriate terminals enclosed in a box complying with the relevant part of BS EN 60670 series or BS 4662
(ix) A device for connecting a luminaire (DCL) outlet complying with BS IEC 61995-1
(x) An installation coupler complying with BS EN 61535.
NOTE: In suspended ceilings one plug-in lighting distribution unit may be used for a number of luminaires.
Seems like just about everything is covered.
Reply to 559.5.1 18th Ed. p219 Luminaire fixed connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
I was away at the weekend & the electrician came round to fix something. While there he decided to condemn an outdoor electrical light as he said...
Working on an industrial radial lighting circuit, 6 son high bay fittings each connected from a conduit box via a short length of flex from the...
Toneyz
T