My adiabatic maths says that for a 16mm main conductor, assumed Ze of 0.2, 80A 88:3 CPD, k as 115.... the earth only needs to be 3.16mm therefore the 6mm in a 6242YH 16mm is more than sufficient.

Anyone disagree?
 
I haven't worked it out but I suspect your right, and I love the signature haha, thats about 4 or 5 with it now lmao.
 
I love the signature haha, thats about 4 or 5 with it now lmao.

Well, I've no idea what the original 'issue' was on about, but I couldn't help but think of something to add.......
 
Personally i wouldn't dream of installing a T&E cable as the mains supply tails. So this situation would never arise!! lol!!!
 
I don't think he means as the tails fella, as a sub main from a KMF switch or breaker I suspect, and if protected by an 80 amp fuse it is going to be Fine IMO, unless it is tails LOL, then your right haha
 
Yes, sub mains from a KMF in a dwelling where no bonding is needed.
 
I always run a 10mm2 earth with a 16mm2 T&E, I am aware it is not always required, as the OP stated as he worked out the calc and he's more than likely right of course, however so what, whats wrong with adding a 10mm2 earth wire with the run? Um nothing, good practice even if unnecessary IMO, another post we can all slate here for fun :tongue3:
 
Your right MDJ, on installs, but on some occasions where your doing an alteration, it can be simpler doing the calcs, than spending the day running in an oversized or unnecessary separate earth, best practice would suggest 10mm to me tho
 
you wouldn't run a 10mm earth to the cooker switch so why to a sub main? Pointless IMO, of course this is as said no bonding etc required

Although every situation deserves its own design
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Rockingit

Mentor
Arms
Supporter
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
6mm integrated CPC of 16mm 6242Y used for main earth
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Rockingit,
Last reply from
MDJ,
Replies
15
Views
3,615

Advert

Back
Top