Hello All
Can any one provide non sarcastic suggestions as to why an 8.5kw shower has not tripped the 32amp mcb protecting that circuit?
Found this install in a domestic property. It seems to have been there for years, without out issue.
DD
Im just dealing with something similar.
8.5kW on a 30A breaker. This one is actually tripping it, but only if the temperature is high and they spend too long in there.
As in the first post, have a look at appendix 3, page 370 of the new edition of BS7671 and you will see that it is highly unlikely a 32A breaker will trip with a 8.5kW shower (approx 37A-no calculator to hand).
If it's a B type it would need to get to about 46amps before it started to think about tripping.
8.5 kW @230v is about 37A.
See page 370. BBB
Remember a B type breaker only needs to disconnect within .4 seconds at 5 times it's rated current
Like has been expressed, the trip curve characteristics explains why the 32amp doesn't trip but relative to design of the circuit we have a regulation that states small overloads for long periods should not be possible so anyone designing/altering this circuit should never have done that in the first place.
8.5kw shower on a 32amp mcb
DirtyDog368,
Darkwood,