Can any one provide non sarcastic suggestions as to why an 8.5kw shower has not tripped the 32amp mcb protecting that circuit?

Found this install in a domestic property. It seems to have been there for years, without out issue.

Thanks
DD
 
Im just dealing with something similar.
8.5kW on a 30A breaker. This one is actually tripping it, but only if the temperature is high and they spend too long in there.

As in the first post, have a look at appendix 3, page 370 of the new edition of BS7671 and you will see that it is highly unlikely a 32A breaker will trip with a 8.5kW shower (approx 37A-no calculator to hand).
 
If it's a B type it would need to get to about 46amps before it started to think about tripping.
8.5 kW @230v is about 37A.
See page 370. BBB

Remember a B type breaker only needs to disconnect within .4 seconds at 5 times it's rated current
 
Like has been expressed, the trip curve characteristics explains why the 32amp doesn't trip but relative to design of the circuit we have a regulation that states small overloads for long periods should not be possible so anyone designing/altering this circuit should never have done that in the first place.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
8.5kw shower on a 32amp mcb
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
DirtyDog368,
Last reply from
Darkwood,
Replies
17
Views
23,343

Advert

Back
Top