Good afternoon and please go easy with me as. I have recently completed my time with one of the services and now wish to become an electrician. My studies are going well but from time to time I lose my way. The question I'd like to ask based on:
  1. The property in question has a 100amp supply
  2. The original consumer unit is working to more or less full supply/capacity
  3. The customer would like an additional CU to supply a workshop which contains a 5 potters wheels ([email protected])
My thinking is because you are drawing near capacity of the 100amp supply, allowing for diversity, this request would not be a feasible!
Look forward to your valuable comments.
No your question is not to inflammatory at all, it's not a real job, it's a scenario I have thought up which I may come across in the future. I'm asking the question because I would like to know the answer with the help of you experienced sparks. My diversity workings are as follows based on counting the circuits and relying purely on design:
Typical dwelling 100amp supply.
Lighting (Diversity 66% of total current demand)
Ground floor 7 lamps @100w = 700w (700x66=396w/230 = 3amps) 3amps
First floor 6 lamps @ 100w=600w (600x66=396w/230 = 1.72amps) 2amps
Ring finals
Kitchen 100% of current demand 32amps
Ground floor Diversity 40% of current demand=12.8amps 13amps
First floor Diversity 40% of current demand=12.8amps 13amps
Other items
Cooker & Hob 11.5Kw (11.5/230=50amps) (first 10+30%remainder no socket) 22amps
Immersion 3Kw (3000/230=13amps) no diversity allowed 13amps
Total 98amps
Ps: With a Shower
Shower 8.5Kw (8000/230=37.8amps) no diversity allowed 38amps
New Total with a shower 135amps
As a trainee I would appreciate constructive help please.
@OP. what you need to do is calculate a sensible average load. rule of thumb is add up the MCB ratings and x 0.4. even so, that will be , IMO, pessimistic. without shower, oven, or washing machines and the like running, we rarely see more than 4A ( < 1.0kW ). even with heavier loads, must of which are running at max. are only so for short periods. e.g. a washing machine will be rated @ about 2.2kW, but that's only when it's heating the water. otherwise it's a 1/4 hp motor only.
Thanks for the advice, yes I'm a real believer in common sense and the like. In today's modern world of electrics can we still apply rule of thumb and will it be accepted by the various CPS providers? or must it be by design and BS7671?
As a trainee sparks I'm starting to think maybe plastering would of been an easier career option Lol :banghead:
With a real world installation you'd simply measure the maximum and average demand over a time period using some sort of data logging meter, probably for a period of two weeks or so, if you aren't sure or need to be accurate.
East Yorks
Business Name
Electrician and More....
Adding a consumer unit.
Ginner,
Ginner,