i tell you what...

lets cut off all the BS1363 plugtops off every appliance shall we....

then we can get a sh1tload of FCUs....start banging em into the wall whereever needed...

should do the trick...rite?

and while we're at it, put each on it's own radial from a 48 way CU.
 
lights need RCD so 3 needed. for bathroom. May as well change board, but its a submain and 16mm feed clipped then runs into wall so 100mA RCD too I think. Starting to add up.

I'm confused by this post, and most of the thread. Did we find out if the boiler is in the bathroom yet ?
 
lights need RCD so 3 needed. for bathroom. May as well change board, but its a submain and 16mm feed clipped then runs into wall so 100mA RCD too I think. Starting to add up.


Hi penmog

don't get carried away trying to retro fix everything to the latest regs, if theres a sub main to the board.... Well there it is. You don't necessarily have to go making everything perfect. Depends what your remit is of course.

s.
 
They have an old crabtree board no RCDs. No space and can't add RCBOs. They want a new bathroom. Cables sound and will upgrade bonding. So have to change board or add RCD spurs. The boiler is not in bathroom but wondering if have to improve circuit to add to it. So boiler ok- thanks. Relieved don't have to retro fit 100mA on submain. Thanks S
 