I would think when it initially starts up it draws more amps too, albeit for a split second. but cutting something and testing is deffo a must for a try result
 
Hi farm, for what it is worth I was doing some current readings on a carpentry workshop and I soon noticed the current jump up when they turned on a big ban saw, approx 40A obviously depends on motor size etc but don't be surprised if this Is the case. Hope this is of some use :£
 
Hi farm, for what it is worth I was doing some current readings on a carpentry workshop and I soon noticed the current jump up when they turned on a big ban saw, approx 40A obviously depends on motor size etc but don't be surprised if this Is the case. Hope this is of some use :£
Just to add here are you talking about inrush or running current here.. unless you have a good quality ammeter with high sampling rates and peak lock you probably wont be able to get a true inrush reading from your meter and could in some cases be hundreds of amps out.
 
How on earth did some of you qualify?? LOL!:yes: That MCB is there to protect the cable... therefore after calcs etc. that cable MUST be rated higher than the MCB regardless of the machine / appliance on the end of it!! Simples!! :17:
 
How on earth did some of you qualify?? LOL!:yes: That MCB is there to protect the cable... therefore after calcs etc. that cable MUST be rated higher than the MCB regardless of the machine / appliance on the end of it!! Simples!! :17:

You are correct to a point but il put this to you i have a 6mm supply 3ph 32amp to a commando style industrial 5pin socket.... if i plug a machine into it with a flc of 17amps can i use 2.5mm flex on a 32amp trailer plug?

Also other exceptions are can be used where the front end device afford only S/C protection with relation to a dedicated circuit supplying a load that by nature of design cannot overload.

So the MUST you so loudly typed is not the case but generally you are correct.
 
You are correct to a point but il put this to you i have a 6mm supply 3ph 32amp to a commando style industrial 5pin socket.... if i plug a machine into it with a flc of 17amps can i use 2.5mm flex on a 32amp trailer plug?

Also other exceptions are can be used where the front end device afford only S/C protection with relation to a dedicated circuit supplying a load that by nature of design cannot overload.

So the MUST you so loudly typed is not the case but generally you are correct.

Ok, Back to basics... Completley ignore the saw.

Remember at collage you did cable calcs?? If there is a 32A mcb infront of this circut ALL wiring in this circuit MUST be rated @ atleast 32A after calcs (fault conditions) unless it is fused down to a lower ampage before dropping cable size.

So you have 3 options... 1 - Replace the MCB for a smaller one.. maybe a D type if its heavy on start up. OR 2 - Replace the socket with a 16A fused isolator Or 3 - upgrade all cables to a suitable size to handle 32A (6mm depending on length of run / referance method etc)

:17:
 
433.3.1 (ii) i mentioned this earlier and depending on your interpretation of this may allow the reduction, also 430.1 note 4 allows flexes plugged into a socket to have a reduced cable size as long as the load characteristics means it cant overload as chapter 43 dosn't cover this area so they are not subject to it.

I only brought this up because the nature of the OP question may allow for such an option .. although agreeably id simply de-rate the front end device if an option but OP cant give us the kw rating of the motor so its the other options we were persuing as de-rating the mcb may give nuisance tripping whether it be a ((c) or (d) used.

I gave you this random example so you may be able to see that what you said isnt strictly true you promoted the word MUST which means to me on no occasion but using this ommision the OP has another option as the nature of the saw will ensure that an overload cannot occur.
 
Last edited by a moderator:
Well Top-Spark i saw that you were viewing my post 37 reply and its you who patronised me with 'remember the college calcs you did' and the 'back to basics' so would be nice to see your response ... im in the mind on this forum that th regs are interpreted sometimes in different ways hence i replied to your post ('How on earth did some of you qualify') although this wasn't aimed directly at anyone but the general theme of replies i was one who suggested out of the usual context of the protective device should always be a lower rating than the ccc of the cable (calcs included)... so i responded now i dont take anything personal and use this site to keep my knowledge sharp but it would be nice to get a response to the last post i did and your interpretation of it ....hey i may be wrong or you may be but everydays a school day on here.

Il put this out there that the OP's case is a 50amp mcb with 10mm 3ph supply to an isolator (all complying); you wire in a machine with a 2.5mm direct to the isolator but dont fuse down but the characteristics of the machine means the 2.5 can't ever overload due to control fusing and overload protection on the motor, as long as the ELI complies with the regs at the machine then how is this non compliant so in respect the OP could directly wire the 2.5mm load connection cable to an isolator with 10mm supply cable and front end 50amp mcb.

This is up for all to debate and please back up with where excactly the danger or non compliance exists.
 
Last edited by a moderator:
I think it's worth mentioning that the reduced cable size must have a sufficient thermal withstand to cope with a short circuit, when fed from an MCB with a higher ampacity than the Iz of the cable.
this is checked with the adiabatic.
 
I think it's worth mentioning that the reduced cable size must have a sufficient thermal withstand to cope with a short circuit, when fed from an MCB with a higher ampacity than the Iz of the cable.
this is checked with the adiabatic.
i have said this that it must comply with the requirements of section 434 in an earlier post regarding fault protection.
 