dan86
I would think when it initially starts up it draws more amps too, albeit for a split second. but cutting something and testing is deffo a must for a try result
Just to add here are you talking about inrush or running current here.. unless you have a good quality ammeter with high sampling rates and peak lock you probably wont be able to get a true inrush reading from your meter and could in some cases be hundreds of amps out.Hi farm, for what it is worth I was doing some current readings on a carpentry workshop and I soon noticed the current jump up when they turned on a big ban saw, approx 40A obviously depends on motor size etc but don't be surprised if this Is the case. Hope this is of some use![]()
How on earth did some of you qualify?? LOL!:yes: That MCB is there to protect the cable... therefore after calcs etc. that cable MUST be rated higher than the MCB regardless of the machine / appliance on the end of it!! Simples!! :17:
You are correct to a point but il put this to you i have a 6mm supply 3ph 32amp to a commando style industrial 5pin socket.... if i plug a machine into it with a flc of 17amps can i use 2.5mm flex on a 32amp trailer plug?
Also other exceptions are can be used where the front end device afford only S/C protection with relation to a dedicated circuit supplying a load that by nature of design cannot overload.
So the MUST you so loudly typed is not the case but generally you are correct.
i have said this that it must comply with the requirements of section 434 in an earlier post regarding fault protection.I think it's worth mentioning that the reduced cable size must have a sufficient thermal withstand to cope with a short circuit, when fed from an MCB with a higher ampacity than the Iz of the cable.
this is checked with the adiabatic.

No offense taken nice to see someone bring it up of the cuffSo you did
that will teach me not to scan read!