I've seen BG leave work,worse that the OP'sBG guy found the fault now there is a thing.

Yes, the swapped tails is the cause (as seen in the later photos).I would like to know if this is what is causing the fault I am experiencing and if this is dangerous? Everything seems to be working
It is pretty rough.The existing consumer unit appears to be a Proteus and the RCD has apparently failed (and been replaced)#
I would suggest a test and a new consumer unit as a minimum, very dodgy to leave as is.
Good choice.I use Hager units as they have parts available for a long time
First as all have said your board is a disaster to start with. as for your mains tails from the meter whoever installed them made a mistake as the inner insulation does not go to the correct terminals but if you look at the meter the Live connections are on the outside of the four with Neutral being the middle two. They do not look as if they are wrong polarity but the wrong mains tail in the connectors. Your quickest and reliable way is to go to B&Q or Screwfix and buy a socket tester that tells you polarity is right or wrong. If wrong you need a qualified electrician to look at your installation ASAP. I am a qualified electrician retired who worked in industrial all my working life I do have my Test and Inspection C&G B.S.7371 and CompEX certification and would never allow anyone to leave an installation like yours. Your RCD is upside down therfore will not trip in the fault condition as your load is on the incomer and will not see the fault. Remember any work now carried out on your main board will have to meet regulations and your Proteus plastic board certainly does not.Thanks for all your input, I'm gonna find a local electrician to check the whole installation as some of you have pointed out there could be other faults by looking the way the consumer unit was wired. It has been this way since I moved in to the property and no work has been done on it since. I would never have known there was a fault had it not been for the British gas guy that tested my sockets.
Thanks again and I wish you all a very happy and prosperous new year.
Solly
I think you need to brush up on how an RCD works.Your RCD is upside down therfore will not trip in the fault condition as your load is on the incomer and will not see the fault.
the plastic board may or may not be suitable for the installation.Remember any work now carried out on your main board will have to meet regulations and your Proteus plastic board certainly does not.
Hi James just to say no I do not need to brush up on how an RCD works but any electrician who takes pride in his work would not put the RCD upside down. I agree it still will work but not very nice to see. If anyone who worked for me were to install upside down any breaker his work mates would have ripped him a new one and there were a good few electricians.I think you need to brush up on how an RCD works.
this statement is quite Simpley wrong.
the plastic board may or may not be suitable for the installation.
just because it is a plastic cover does not mean that it must be replaced in most circumstances.
however, many of the problems seen would easily be fixed by replacing the consumer unit for a modern one with the correct breakers inside.
Hi James just to say no I do not need to brush up on how an RCD works but any electrician who takes pride in his work would not put the RCD upside down. I agree it still will work but not very nice to see. If anyone who worked for me were to install upside down any breaker his work mates would have ripped him a new one and there were a good few electricians.
As for the Board being plastic they are illegal to install now due to fire brigade recommendations. If anyone were to work on that board they would be required by regulations to use PUEWR as there guide and install a manufactured metal DB. As when there was fires these could and did put out Heavy black toxic smoke.
My personnel dealings with Proteus equipment has not been good and I personally would never recommend the brand to anyone, but again that is my opinion
if that's the case, then a read up of the regs.is a good idea, i said regs., not the napit joke book.Are you saying if someone does any work in a plastic consumer unit then they must change it to a metal one?