Three types of Hazardous Areas are recognised as follows:
• Group II - Hazardous Areas (gas or vapour) in which an explosive atmosphere is present, or may be expected to be present, in quantities such as to require special precautions for the construction, installation and use of the equipment.
• Group III - Hazardous Area (dust) in which combustible dust in cloud form is, or can be expected to be present, in quantities such as to require special precautions for the construction and use of equipment in order to prevent ignition of an explosive dust/air mixture.
• Explosives Hazardous Areas – An area in which explosives material/substances of Explosives Ordnance are exposed to the atmosphere such that they require special precautions for the construction and use of equipment in order to prevent ignition of an explosives material/substance.

sound suspiciously like the material your working with... These rules don’t just apply to the Oil & Gas and offshore industries mate.
 
Last edited:
Update: I just checked, it appears Unitrunk only sell direct from their own places, and there's no central tel number, only published (massive) list prices and an email form. They appear to be one of those companies which makes it hard to buy from them. Marketing
Some others also do socket fittings. You might have more luck with this:

I found it easy to get the Unitrunk stuff from Holland House (oddly enough a Scottish electrical trade suppler, one of the oldest).
 
Last edited:
Three types of Hazardous Areas are recognised as follows:
...
• Explosives Hazardous Areas – An area in which explosives material/substances of Explosives Ordnance are exposed to the atmosphere such that they require special precautions for the construction and use of equipment in order to prevent ignition of an explosives material/substance.

sound suspiciously like the material your working with... These rules don’t just apply to the Oil & Gas and offshore industries mate.

Eh? Where did that badly-written rubbish come from?

I've been working with this stuff for 40 years but have never read that before.

I can't believe that's from a UK or European document. Whichever genius wrote '... explosives material/substances of Explosives Ordnance are exposed to the atmosphere [sic] ...' clearly has no experience of working with energetics.

That is a fine example of exactly the kind of nonsense that gets into the literature, then is parroted by an enforcing authority without understanding. I'm not having a go at you, mate, but I've been dealing with this 'legislative' cr@p for decades and it irritates me :)

In the UK we have the HSW Act, and the subsidiary SI 2014 No. 1638 The Explosives Regulations 2014.

In essence they require you to take reasonable precautions, considering all the circumstances of each case. Therefore the requirements are very different if you wish to set up a nitroglycerine factory producing 1000 tonnes a year, and if you want to hold a few grams in an experimental lab for a day.

Excuse the rant, but essentially my policy is to identify actual risk (in this case static sparks) then to use common sense.

Only rarely do flames shoot out of 13A sockets. Or at least from those which I wired they don't.

So far :D
 
Well that’s straight from the compEX list of definitions. A standard used by every global Hazardous area company, and no offence I know which argument I would believe. OK. Your dealing with “Grams” irrespective of large factories. Your Duty of care is to ensure that your install ensures that the risk is ALARP. I wouldn’t be reliant on a 13amp B&Q socket for that.
 
..Do have a vague memory of an Electrostatic Field detector .. that would would wail with big field changes , down side was it used handpicked CMOS inputs
left in a ZAPABLE open circuit state + attached to paddle antennas ..
(but I'll have to trawl internet history from pre 1998 )
( Moving any midly conductive object in an electric field --Can add energy to its stored charge - An induction technique )
... capacitively detecting any charges moving about nearby .... assuming no strong AC fields upset it.
(any missing -r-s due to iffy keyboard.)
 
Well that’s straight from the compEX list of definitions. A standard used by every global Hazardous area company, and no offence I know which argument I would believe. OK. Your dealing with “Grams” irrespective of large factories. Your Duty of care is to ensure that your install ensures that the risk is ALARP. I wouldn’t be reliant on a 13amp B&Q socket for that.

Oh well, I tend to believe the opinion of someone who’s actually worked with live explosives for 40 years and still has all appendages attached. Now where would I find one of them? ;)

I’m interested by what mechanism you believe the presence of an empty and shuttered quality 13A metallic socket could cause the ignition of say 5g of nitrocellulose in a crucible a metre away. If there’s something I don’t know I genuinely want to learn. I’m a scientist by nature and training: the only thing a scientist knows for certain is that he or she doesn’t know much.

I accept that many guidelines are there to be idiot proof. Eg exclude sockets so no fool can plug in a soldering iron or fan heater. But I will be excluding not only static from my lab, but fools as well.

ps. What’s compEX? I’ve never heard of it. :)
 
Oh well, I tend to believe the opinion of someone who’s actually worked with live explosives for 40 years and still has all appendages attached. Now where would I find one of them? ;)
As Derek Lowe put it:

Hexanitro? Say what? I’d call for all the chemists who’ve ever worked with a hexanitro compound to raise their hands, but that might be assuming too much about the limb-to-chemist ratio.

I accept that many guidelines are there to be idiot proof. Eg exclude sockets so no fool can plug in a soldering iron or fan heater. But I will be excluding not only static from my lab, but fools as well.
That is a factor for this forum - what sort of load(s) are you planning?

To my untrained eye with explosives, keeping the opportunities for electrical incidents down is a starting point, and then taking steps to limit the worst-case let-through energy if there is a fault, the second step.

For example, if you have no loads above 5A or so, you might chose a few radial sockets with 10A MCBs for your "13A" sockets, and have the whole system backed up by, say, a 32A BS88 fuse as an ultimate energy-limiter compared to MCBs at high fault currents.
 
Well that’s straight from the compEX list of definitions. A standard used by every global Hazardous area company, and no offence I know which argument I would believe. OK. Your dealing with “Grams” irrespective of large factories. Your Duty of care is to ensure that your install ensures that the risk is ALARP. I wouldn’t be reliant on a 13amp B&Q socket for that.
Tell you what though, I’d be with you when it comes to major storage magazines. I’ve just watched a video from Beirut today. That was one astounding bang, the shockwave created its own meteorological effect. I reckon that was tens, if not hundreds of tonnes of HE, all going off at once. Not ideal.
 

Reply to Advice on designing an electrostatic-proof building please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably...
Replies
13
Views
2K
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always...
Replies
36
Views
8K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
This is my first posting here - I am not an electrician so please bear with me. I am trying to establish the best method to provide earthing of a...
Replies
12
Views
4K
Evening, Im working for a builder on a kitchen extension.. Now the usual procedure with this building contractor is do the essential checks...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock