Mark42
Patron
I’m converting a steel Portacabin-type box into a lab for static-sensitive equipment and materials.
If there are any ESD gurus on here, I’d appreciate any advice please!
I’ve ripped out all the vinyl, floored it with aluminium treadplate, clad the walls in painted aluminium sheets, and left the ceiling in the original painted steel.
Worktops will be in Trespa anti-static material, there’s a metal fume cupboard, and metal cupboards and shelving. Everything is bonded together, and earthed TT. Earth impedance is good.
I’m also intending to run a bonded metal (copper or maybe ali) strip all round the worktops, with little sockets for plugging in flying earth leads for loose equipment, wrist straps and so on. Conductive shoes will be worn, and no plastics or other insulators allowed in the building.
But this is all new to me: have I missed anything? The most dangerous errors are those you don’t know you’ve made!
And one specific question please:
Is it OK to use 10mm John Guest plastic plumbing pipe (Polybutylene), tucked away under the worktops? I need to run ring mains of mains water, Type 2 pure water, vacuum, and gas. There are no great flow velocities. It’s so much nicer to install, and easier to amend. Is a little bit of plastic pipe which will never be touched really a problem?
You might find the floor is mostly wood over some steel cross-beams, so make sure the building is Earthed to the ground immediately below to keep ant E field down from that source.
Keep the place humidified (within reason) to lower any charge build up of stuff you have not thought about.
Folk moving about are a significant source, so you will have to take care of the types of clothing worn (i.e. keep to natural fibres like cotton/wool and not polyesters, etc) or have semi-conductive overalls.
If worried about the pipes (and flow in an insulators is a risk) then look to screening them by having a mesh cover under the worktops or possibly look at conductive paints, but they won't stick terribly well to plastic, etc. To be honest going for copper pipes and equipotential bonding them is a far safer choice if you need to keep E fields down through materials like wood, or anti-static plastics that are barely conductive (static dissipative), etc.
[automerge]1596438151[/automerge]
Doh, just re-read and you have conductive floors already!
[automerge]1596438453[/automerge]
If it is more than just low electric fields (i.e. you are trying to avoid sparks, etc) then you need to look also at tools and those tend to be expensive for stuff made from beryllium-copper alloys.
Same applies for electrical switches, motors, etc, you would need to look at intrinsically safe ones designed for explosive atmospheres.
There are probably some folk with experience in the oil industries who can tell you more about such standards & practices.
[automerge]1596438887[/automerge]
Also for wiring you would be looking at stuff in metal trunking, metal conduit, SWA cable, or far simpler to handle using Flexishield cable so all circuits are within an earthed shield. Strip lights, etc, might need to have CPC-bonded wire mesh over them depending on how much field you can tolerate.
Speak to a company called Vermason.
Consider air ionisers. Also they will need to regularly test things like foot straps and wrist straps, so a tester will be needed. Probably down to them that though.
Have the electrical supply isolated from the mains, M/A set or Isolating transformers. insulate both inside and outside, use wave guides for any entry point to the building.
Raise the building floor from the main floor, air condition to a70deg and 50% RH or as near as possible, use DP mcbs etc.
I wouldn't have thought that most of that would be needed for an anti static environment.
You might find the floor is mostly wood over some steel cross-beams …
Exactly correct. It’s pretty rubbish construction actually. I’m adding 25mm Celotex, then a 3mm ali treadplate floor glued down, with bare aluminium wires laid underneath the sheets, all terminated at a main bonding point. I’ve no idea if this is a standard way of doing things, I made it up.
… Keep the place humidified (within reason) to lower any charge build up of stuff you have not thought about. …
Great idea.
… have semi-conductive overalls …
Yes, we’re doing that.
Exactly correct. It’s all about preventing sparks. The lab is for sensitive explosives.
I think there’s no need for that as it’s for solid explosive materials sitting on a desk on in a flask, not explosive atmospheres, which is an entirely different thing.
Flexishield is a great idea. Thanks. It appears you can’t buy cut lengths so I’ve ordered one roll of 2.5 which I’ll use for everything (inc lighting!)
The easiest installation would be one run of dado-rail multi-compartment trunking around the walls, terminating directly into the DB. I’m researching this today. It appears a metallic version is very difficult (and expensive!) to source. Or I'm thinking quality 100 x 50 metal trunking, with accessories cut into the lid, which is economic enough and fully shielded, but would look a bit sh!te :)
I was going to use 3 No. LED IP-rated strips, the type with all the electronics in a metallic enclosure.
I need to keep the cost down so I’m not looking at intrinsically-safe equipment unless I really need to.
… If worried about the pipes (and flow in an insulators is a risk) then look to screening them by having a mesh cover under the worktops or possibly look at conductive paints, but they won't stick terribly well to plastic, etc.
Agreed but there are other reasons why copper is not a good idea, chemically. Many of the regs for this kind of thing were written sometime in the Cretaceous (probably by actual dinosaurs), before plastic pipework existed. I’ll do some research on the static properties of John Guest pipes, which are either polybutylene or polyethylene first.
I like your metal cage idea, that’s cheap and easy to fabricate.
Thanks for the excellent advice!
I'll post photos once it's done in a few weeks ...
Ah, in your OP you said it was for static sensitive equipment. I assumed they were repairing electronic equipment. I see it's actually explosion risk you are looking at. That's a whole different ball game with it's own regulations.
... If worried about the pipes (and flow in an insulators is a risk) then look to screening them by having a mesh cover under the worktops ...
Any idea how dense a mesh cover needs to be to provide electrostatic screening? Would something as simple as bonded mesh cable basket hung on wall clips, directly over the runs of plastic pipes work?
Very easy to buy and fit. If cut into short modules, easy to unclip to make changes to the push-fit pipework.
It would also prevent touching, so even if the pipes carried an electrostatic charge, it can't go anywhere?
I do like simple solutions :)
I have a strong suspicion that is likely to be a rather controlled occupation. Getting advice from a bunch of randoms on an internet forum is not something you can depend upon!
It is half way between SWA and normal round cable to work with. It tends to stay in place when you bend/set it. It is not "flexible" - it is intended for fixed wiring. However, unlike SWA where you need to carefully fit a gland for the outer armour/CPC, for Flexishield you can use a normal IP68 style plastic gland so far easier to use.
Read the stripping instructions, basically you score the outer sheath and then bend it to split the plastic and aluminium foil, then pull it off. With gloves, and some force.
You can score with a knife if careful, but this sort of tool is far safer & repeatable:
Unitrunk make covers for the 100mm and 150mm wide trunking pre-punched for single and double switches/sockets:
While trunking is hard to work with, it is touch and long-lasting. Just remember to use grommets and/or glands for cable in and out, and to ensure it is bonded to your MET.
As you found, also massively cheaper than metallic dado rail style options.
Or wrap it in aluminium self-adhesive tape.
We look forward to seeing it.
Also we can discuss where you are likely to appear next:
  • Derek Lowe's blog "Things I Won't Work With"
  • The Darwin Awards
Ladies, gentlemen, and internet randoms, place your bets :)
pc1966 there a lot of "RANDOMS" on this forum that have a lot of knowledge, judging from your reply you think are insignificant, chose your wording carefully.
Sorry if I offended anyone, that was not my intention.
It was more the point that if the excrement were to impact on the air-moving apparatus, standing up in a court and saying "But the folk on forum XYZ said this was safe!" is not going to go down well.
Is this a licenced explosives factory?
If it is then I know what the OP means about the rules being antiquated, our fireworks business has a factory licence, the explosives factories act of 1875 is the appropriate law. Although it has been updated a few times since then!
Close. The Explosives Act 1875, AKA 'The Green Book' written by the rather splendid Col. Majendie. I've had my copy for over 40 years. Beautiful, precise law which nearly all made sense. Now almost entirely repealed and replaced by a succession of European-inspired Acts and Statutory Instruments which are impenetrable, daft in parts, and contain typos.
And yes, this is an authorised explosives site, it's what I do. (Electrickery is an adjunct, primarily for personal use).
You're in the fireworks business? We must know of each other. CBI EIG? IExpE?
[automerge]1596493087[/automerge]
Brilliant. Well-found! Doesn't look too bad either. A bit of etch primer and a coat of paint and it will both look pro, and save me a few quid :). Thanks for the tip.
Good idea. Or stainless cable braid as used on vehicle fuel hoses. And I just found this:
:D
Metallised spiral wrap for use in the food industry. I've e-mailed the manufacturer to ask it it's actually conductive and hence anti-static.
Would be dead easy to install.
... Also we can discuss where you are likely to appear next:
Derek Lowe's blog "Things I Won't Work With" ...
Is that the bloke with the azidoazides which go off if you 'look at them in a funny way'?
Ha Ha, bloody amateur. Here is me enjoying destroying heavily peroxidised Tetrahydrofuran found earlier this year in a Kent lab. A fine day out. Yeah, and now I'm waiting for a chorus of, 'All the gear but ...' :D
I do rather enjoy my work.
... Getting advice from a bunch of randoms on an internet forum is not something you can depend upon!
Wrong.
I have much more respect for people like those on this type of forum who, like me, actually build stuff than for any number of supposed 'experts' who have done little but read the manual. And I often find those enforcing regulations read the manual only yesterday.
And advice sought does not always have to be taken ;)
I know photon energy gets involved in some unstable reactions ,maybe we can include quantum mechanics for if some-one was actually looking/filming ..satellite passing over !
(when a good conductor can meet another conductor )-- 500k -1 M in all sockets could reduce arc from a hand held metal object waved too near a socket... always a compromise between discharge time and reducing current in any small arc ! -- I'm no expert but was wary of being personally earthed
with anything lower than 1MOhm.
Good ideas in both cases.
Yes, his articles are both informative and amusing, with the ones on hideous chemicals usually the best of both:
[automerge]1596522555[/automerge]
Wrong.
As long as you understand things and filter the advice it is fine!
This forum has a policy of avoiding step-by-step guides for DIY and being very cautious about any advice on the USA forum, etc, to avoid it coming back to bite them if it all goes horribly wrong and things get litigious.
[automerge]1596523037[/automerge]
Also to add you probably will need the building to have a lightning conductor arrangement, at least all explosive stores I have seen have that.
And relating to that is having SPD fitted to the incoming distribution board. With a lighting conductor in use it should be a Type 1+2 to deal with the much higher surge energy in the event of a direct hit (not just induced spikes) and they cost a lot more (single phase in the £300 region, not the £70 region for Type 2 only). Examples include:
[automerge]1596523217[/automerge]
I'm no expert but was wary of being personally earthed with anything lower than 1MOhm.
Quite right, most ESD wrist earth straps are of the order of 1M for that very reason! For example:
Also in such environments it is not uncommon to use 10mA RCDs as well just to lower the risk further.
:D
Looks interesting!
Did you buy the suit off the guy from Boney M?
OK, that's enough reminiscing :). I'm ordering trunking to use as dado rail today.
Unitrunk looked excellent, until I looked at the price: 100 x 50 x 3m is £193! I though it was a typo.
Very similar Tamlex 100 x 50 x 3m from CEF is £24.17.
I'd have to cut my own holes in the Tamlex, but for an overall saving of £1,012 (!) I think I'll get the jig saw out
That is the list price. Most electrical trade places will give you discounts of the order of 70-90% on that if you ask the right folk.
[automerge]1596528738[/automerge]
If your company are doing a lot of this sort of work (internally, not as electrician services, etc) it might be in your interests to apply for a trade account with one or two of the local wholesalers.
[automerge]1596528945[/automerge]
Is the trunking just for a set of 13A sockets? you might find it easier to use the likes of these and glands/Flexishield between them:
If you have explosive material or potential to become explosive then you’ll first need to follow Hazard area classification depending on what chemical or potentially explosive Material you are using. Normally cabling would Have to be intrinsically safe ie the use of shunt diodes or enclosures would have to be EX rated depending on the application. EX D is flameproof, EX P is pressurisation of an enclosure. EX E is extra protection and so on. Zoning is generally 0,1 and 2 and that basically goes on your LRL & URL limits.
Thanks for the ideas, but those regs are for explosive atmospheres, as often found in chem plants, or offshore. It has nothing to do with explosive substances. It's a very frequent confusion, especially among regulators.
Think about it - a sparky switch would definitely ignite a gas/air mixture permeating the whole area, but the same sparky switch would not jump across a room and set off a pile of nitrocellulose propellant sitting on a lab bench. It's only static protection which is important to consider in the latter case.
[automerge]1596533604[/automerge]
That is the list price. Most electrical trade places will give you discounts of the order of 70-90% ...
Yeah, it's stupid isn't it? Like arguing with Travis Perkins. We do have trade accounts and I'm good at getting best prices, but not many places advertise the Unitrunk stuff, so it's perhaps too much effort.
Update: I just checked, it appears Unitrunk only sell direct from their own places, and there's no central tel number, only published (massive) list prices and an email form. They appear to be one of those companies which makes it hard to buy from them. Marketing people call this having a 'customer prevention department' :rolleyes: I can't be bothered! cf. Two clicks on CEF and Tamlex product can arrive tomorrow ...
Is the trunking just for a set of 13A sockets? ...
No, it's for power, data, telelphone and a DC lab supply as well. Hence the flexibility of using trunking.
Three types of Hazardous Areas are recognised as follows:
• Group II - Hazardous Areas (gas or vapour) in which an explosive atmosphere is present, or may be expected to be present, in quantities such as to require special precautions for the construction, installation and use of the equipment.
• Group III - Hazardous Area (dust) in which combustible dust in cloud form is, or can be expected to be present, in quantities such as to require special precautions for the construction and use of equipment in order to prevent ignition of an explosive dust/air mixture.
• Explosives Hazardous Areas – An area in which explosives material/substances of Explosives Ordnance are exposed to the atmosphere such that they require special precautions for the construction and use of equipment in order to prevent ignition of an explosives material/substance.
sound suspiciously like the material your working with... These rules don’t just apply to the Oil & Gas and offshore industries mate.
Some others also do socket fittings. You might have more luck with this:
I found it easy to get the Unitrunk stuff from Holland House (oddly enough a Scottish electrical trade suppler, one of the oldest).
Eh? Where did that badly-written rubbish come from?
I've been working with this stuff for 40 years but have never read that before.
I can't believe that's from a UK or European document. Whichever genius wrote '... explosives material/substances of Explosives Ordnance are exposed to the atmosphere [sic] ...' clearly has no experience of working with energetics.
That is a fine example of exactly the kind of nonsense that gets into the literature, then is parroted by an enforcing authority without understanding. I'm not having a go at you, mate, but I've been dealing with this 'legislative' cr@p for decades and it irritates me :)
In the UK we have the HSW Act, and the subsidiary SI 2014 No. 1638 The Explosives Regulations 2014.
In essence they require you to take reasonable precautions, considering all the circumstances of each case. Therefore the requirements are very different if you wish to set up a nitroglycerine factory producing 1000 tonnes a year, and if you want to hold a few grams in an experimental lab for a day.
Excuse the rant, but essentially my policy is to identify actual risk (in this case static sparks) then to use common sense.
Only rarely do flames shoot out of 13A sockets. Or at least from those which I wired they don't.
So far :D
Well that’s straight from the compEX list of definitions. A standard used by every global Hazardous area company, and no offence I know which argument I would believe. OK. Your dealing with “Grams” irrespective of large factories. Your Duty of care is to ensure that your install ensures that the risk is ALARP. I wouldn’t be reliant on a 13amp B&Q socket for that.
..Do have a vague memory of an Electrostatic Field detector .. that would would wail with big field changes , down side was it used handpicked CMOS inputs
left in a ZAPABLE open circuit state + attached to paddle antennas ..
(but I'll have to trawl internet history from pre 1998 )
( Moving any midly conductive object in an electric field --Can add energy to its stored charge - An induction technique )
... capacitively detecting any charges moving about nearby .... assuming no strong AC fields upset it.
(any missing -r-s due to iffy keyboard.)
Oh well, I tend to believe the opinion of someone who’s actually worked with live explosives for 40 years and still has all appendages attached. Now where would I find one of them? ;)
I’m interested by what mechanism you believe the presence of an empty and shuttered quality 13A metallic socket could cause the ignition of say 5g of nitrocellulose in a crucible a metre away. If there’s something I don’t know I genuinely want to learn. I’m a scientist by nature and training: the only thing a scientist knows for certain is that he or she doesn’t know much.
I accept that many guidelines are there to be idiot proof. Eg exclude sockets so no fool can plug in a soldering iron or fan heater. But I will be excluding not only static from my lab, but fools as well.
ps. What’s compEX? I’ve never heard of it. :)
As Derek Lowe put it:
Hexanitro? Say what? I’d call for all the chemists who’ve ever worked with a hexanitro compound to raise their hands, but that might be assuming too much about the limb-to-chemist ratio.
That is a factor for this forum - what sort of load(s) are you planning?
To my untrained eye with explosives, keeping the opportunities for electrical incidents down is a starting point, and then taking steps to limit the worst-case let-through energy if there is a fault, the second step.
For example, if you have no loads above 5A or so, you might chose a few radial sockets with 10A MCBs for your "13A" sockets, and have the whole system backed up by, say, a 32A BS88 fuse as an ultimate energy-limiter compared to MCBs at high fault currents.
Tell you what though, I’d be with you when it comes to major storage magazines. I’ve just watched a video from Beirut today. That was one astounding bang, the shockwave created its own meteorological effect. I reckon that was tens, if not hundreds of tonnes of HE, all going off at once. Not ideal.
Mark42
Patron
UK
Other
Advice on designing an electrostatic-proof building please.
Mark42,
nicebutdim,