Personally, I think the report is clutching at straws to get extra work.
Why do I say that....
Item 1. The 18th edition does not 'require' cables to be buried more than 50mm.
Item 8. Main earth undersized. If there is evidence of thermal damage, I'd C2, but with no evidence I'd C3 it.
Item 9. Unswitched socket outlet. Show me a regulation unswitched socket outlets contravene.
Item 10. As @telectrix has already pointed out, high earth leakage on circuits where IR is claimed to be >100 Mega ohms.
Just my tuppence worth
Why do I say that....
Item 1. The 18th edition does not 'require' cables to be buried more than 50mm.
Item 8. Main earth undersized. If there is evidence of thermal damage, I'd C2, but with no evidence I'd C3 it.
Item 9. Unswitched socket outlet. Show me a regulation unswitched socket outlets contravene.
Item 10. As @telectrix has already pointed out, high earth leakage on circuits where IR is claimed to be >100 Mega ohms.
Just my tuppence worth