Id bet my 50p that zero dead testing was carried out.
Interestingly, I found the previous EICR,
- it has the r1, rn, r2 values on the ring mains.
- and it had 1mm cable for lighting circuits which I don't believe. This may have just been copied into the new EICR.
- the IR tests on the ring mains and lighting was not done due to "unable to remove all load sockets, lighting had electronic dimmers"

There's still a dimmer upstairs, but it's downstairs lighting that has the supposed earth leakage.
 
If any member of the public post a EICR on here it will be pulled apart by us for the minor things, thats why you have had a big response on here. That report to me is pretty poorly written up, missing information and misleading.

Id ask the estate agent why they recommended him at that price, see if there is a member on here local who will price for the board change and give you a hourly rate of any faults that might be present.
 
Funny thing is if it had no recommendations the op would not be on here saying ‘this EICR cannot be correct. They were only here for 4.5 hours.’
 
  • Agree
Reactions: chris gray
As others have mentioned, the test results, the check list and the observations don't really stack up.

I suspect the person doing the test & inspection doesn't have a proper understanding of what he/she is doing (and shouldn't really be doing this work).
 
Interestingly, I found the previous EICR,
- it has the r1, rn, r2 values on the ring mains.
- and it had 1mm cable for lighting circuits which I don't believe. This may have just been copied into the new EICR.
- the IR tests on the ring mains and lighting was not done due to "unable to remove all load sockets, lighting had electronic dimmers"

There's still a dimmer upstairs, but it's downstairs lighting that has the supposed earth leakage.

I think if previous r1,rn,r2 readings are available then these tests can be omitted if needed.

I'm sure I heard that on the 2391 course. I could be wrong
 
Take the money for the rent but unwilling to spend money to keep the people inside safe.
I actually think the questions are reasonable. The op did not mention that they are not having the work done.
I think for someone who is not an electrician I would expect their initial reaction to be to question the report and the cost if it was not made fully clear to them.

To the OP:
My advice would be to get the C2's completed asap by a qualified competent electrician, then ask if it would be possible to rectify some of the minor issues at a small added cost. Lets face it some of us would do the board change (once any faults had been rectified) and probably throw in the labour cost of changing the socket outlet and the ceiling rose.
Fault finding can be very time consuming, especially on socket ring circuits. There is no way to determine how quick they can be found and/or rectified, so quoting on such is very difficult. I usually explain to my customer and agree to charge a minimum call out, then per hour there after. Please also be aware that the fault/s found could be simple cheap fixes to rectify or potentially costly dependent on the problem. Your electrician will advise you accordingly.
 
I think if previous r1,rn,r2 readings are available then these tests can be omitted if needed.

I'm sure I heard that on the 2391 course. I could be wrong

No. Always test ring continuity on EICR mate as it needs to be confirmed as part of proving if circuit is satisfactory or not.
 
No. Always test ring continuity on EICR mate as it needs to be confirmed as part of proving if circuit is satisfactory or not.

Think there is something about this in one of the books. I'll see if I can find it
 
The install looks not too bad, however the EICR seems pants

You can get immersion thermostats with a built in secondary cut out for about £10-£15, this means the immersion heater can stay with a compliant thermostat

Looking at it s board and bond with a bit of tlc would make all the difference- I would also suggest mains interlinked smoke detectors (I use thew Aico 3000 range) be installed
 
Another wooden top masscaraiding as a electrician
EICR - is it safe for continued use Yes or No
It is not a list of upgrades to bring it to the 18th edition
Why does the electrician not describe what he believes to be an issue and a description of the solution on a separate note. These reports are for laymen who are paying for a Skilled Person to advise them on condition.
Indicates no RCD in bathroom, then indicates supplementary bonding C3?
Not worth the paper it is written on ignore the C2’s until reason for the C2 is explained correctly. Bloke does not know what he is doing.
Earth leakage high just stopped laughing
Ceiling rose needs replacing - is it because enclosure is damaged as 651.2?
 
This is actually mentioned in gn3 if it looks like the ring has not been altered and there are previous test results,however I’d always test it as standard.

Ah yes, that's it.

Personally I would always check but it may be a reason why this person hasn't on this particular EICR
 
This is actually mentioned in gn3 if it looks like the ring has not been altered and there are previous test results,however I’d always test it as standard.

Fair play Ian and Gaz, I've read GN3 enough and couldn't recall that in there. I'll still ignore it and test RFC end to ends everytime though :)
 
Personally I would always check but it may be a reason why this person hasn't on this particular EICR

In this case, most likely because they took Zs's only and made the rest up in the van!!! :)

Earth leakage clamp was reading off the scale probably cause they had it around the line conductor only I expect lol
 
  • Funny
Reactions: DPG and SparkyChick

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Baku, Azerbaijan
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Advice on Unsatisfactory EICR report
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
62

Advert

Thread statistics

Created
naylorpd,
Last reply from
TJ Anderson,
Replies
62
Views
11,419

Advert