I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The install is fine except the earth tag (banjos) haven't been fitted and they have relied on the metal plate as an earth. My question is, can you get a retro fit earth tag or "all in one solution" to earth all of these glands safely without disruption? Im aware of earth nuts but they would still need disconnection of circuits so I was hoping to find another alternative if anybody has any suggestions?
The Wiska E-Nut ones might do the job!
Tap to zoom
Wiska COMBI E-NUT M25 Earthing Nuts (1x M25) With Earth Leads & Screws Brass - E-NUT25​
Quick Find Code: E-NUT25
Free Delivery on orders over £35 (excluding Highlands and Islands)
  • 1 x M25
  • Material brass
  • Earthing nuts (single) for COMBI Junction Boxes, with earthing lead
  • Sold in packs of 5
I did think about these but you would still have to fully disconnect (which I have done anyway now 🙄) so the issue is sorted but now I'm just wondering if there's an actual solution to this issue going forwards when the circuit cannot be disconnected. Doesn't appear to be
No they are split, so can and I have used for exact same scenario you are describing without disconnecting.
Tap to zoom
  • 1 x M25
  • Material brass
Never seen these before. Clever invention
How topical.
I was in <somewhere> only today and the subject of earthing came up - there being a fairly substantial earth ring for the systems being tested, but a requirement for a separate earth for other facility equipment off a different supply. And as I looked down at a metalclad socket with SWA in and out, there was a flylead from one banjo to the other (outside of the box) that didn't go into the socket itself.
I commented on this, and was told that the nut inside is designed to scrape the paint off as you tighten it - so the socket is earthed via that. It wasn't the right moment to "discuss" things further, but I was thinking that if they work then no need for the flylead, and if there's a need for the flylead then not much confidence that they do work.
But, one of the people I was with commented on how on a different installation there was a distribution board with "many" cables in it - and the installers had put the nuts the wrong way round. Apparently they were "rather unhappy" at having to pull every circuit in order to turn the nuts over.
SWA have been making them for years. Pricey, but convenient at times.
The ones for Wiska boxes are very good and Imo is the only way to do a decent job, as it also adds some support to the glands when using this type of box.
Just be aware that with this type of earthing gadget, you tighten the clamping screw down on the threaded part of the gland, which may cause some damage to the threads.
In other words you may be screwed if the screw screws the screw...
The glands do use the thread of the Wiska box, which does give them some strength.
The other alternative is to do a dogs' ear of it and banjo outside, nut and bolt and compress the plastic box to within an inch of its life :)
The OP has a metal enclosure with metal gland plate though doesn't he? And question is around not having to disconnect all the cables to fit an earth banjo/nut
The ops question had already been answered with M20 E Nut.
My post was being informative as some hadn't seen that type of kit before.
You can also get E springs, which maybe of interest to the OP.
Do you have a link to the SWA version?
I'd never heard of Wiska e-nuts, so googled them yesterday and the link I clicked showed a piranha type of nut.
Did the same today, as I was surprised at you asking for a link, and saw very different results. I never seen anything similar and don't imagine SWA sell them.
Uk
United Kingdom
Electrical Engineer (Qualified)
Alternative retro fit earth tag options for SWA?
YanniPap,
DefyG,
