Discuss another contactor question sorry in the UK Electrical Forum area at ElectriciansForums.net

S

super

hi all thanks for any advice,i am looking into installing a contactor to switch multiple lighting circuits i cant find a design current supply needed to switch the contactor in any documents apart from mA ratings, the norm i always see is 6amps which is what i plan to use at the consumer unit to supply the contactor but why is it always taken as 6amps im sure looking at this contactor it requires mA but do we use 6amp mcbs as these are the smallest in general stock? are contactors designed to take a 6 amp supply to switch them over? im having to do a circuit design for the contactor and looking to start with the Ib rating and failed straight away,so only now asking the question after years of installing a 6amp mcb any knowledge very welcome thanks
 
A control circuit could be in place for a single switch to operate a single contactor, or multiple relays and switches and other input devices to operate multiple contactors.
The control MCB should be selected accordingly.

Most of the Industrial / commercial control circuits I've worked on generally have a 2 or 4 amp control MCB or fuse.
 
6A is usually the smallest MCB made by the various board manufacturers, so you choice is a bit limited. Personally I would fit a 2A fuse in your contactor panel for the control.
 

Reply to another contactor question sorry in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
577
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock