Discuss Another EICR RCD question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
John777
Hi All.
Sorry for not introducing myself and asking a question on my firs post, but I have been losing sleep lately...
An electrician went into flat and did EICR. Would not give a copy until I paid up front and now says I need a new fuse box etc £850 + worth of work. My flat is tenanted and in excellent condition. It was built about 20 years ago. The wiring looks safe enough to me (I'm not an electrician tho!) but there is no RCD.
I am lead to believe that it doesn't need to be changed, since no new circuits have been added.
Any advice would be appreciated
@John777
I have removed the certificate you posted as you left all the contractors details on the cert' if you wish to post these reports please ensure all information is fully redacted that can identify the address and contractor.
I would like if you fully redact the info' as opposed to partially doing so like address etc.
On a personal view, I agree with Tel, I would say C3 for lack of RCD, however in general more and more would venture towards C2 these days.
As for the third C2, it would depend on the size of the shower, this could be above 32A but below the cable limit, as it's a fixed load the MCB does not have to provide overload protection so the 40A MCB could be fine as it is.
In saying all the above, replacing the consumer units would be a worthwhile investment.
Looks like it was done pretty decently. A look inside and at the main incomer and tails would be interesting. Might be a fair job for someone decent. You never know, though.
Hi All.
I attach EICR and photo of fuse boxView attachment 84342
  • EICR anon.pdf
To be honest I'm surprised most of those C3s were not C2. What level of the building is the flat located on.
Agree, however without seeing the actual job it is difficult to judge, the FCU in Zone 1 could be a left-over from a heater 2.2m high - I would agree with C3, as realistically there is no issue; if it was next to the bath however then C2 any day.
There are a number of significant errors with the report though - it's shown as C2 for RCDs provided for fault protection - it isn't a TT all circuits appear to have suitable fault protection - so what is this about??? There is a C3 for adequacy of fault protection, yet nothing in the observations regarding inadequacy of fault protection, there is a C2 for lack of overload protection on a shower (which isn't actually needed on a fixed load anyway) and so on.
Not a good example of a periodic inspection, but exceedingly common unfortunately.
I agree they state TN-C-S but the Inspection Schedule states all the first part as LIM which to me indicates the main intake was not accessed, overall that Schedule is not good. Open continuity of ring final circuit conductors I will always C2, overheating at shower switch the same and open connectors at the HW pump would have to see but sounds to me a C2.
As already mentioned this is one of those cases where although there are several errors on the schedule, it may well still end up having at least one C2 and a new consumer unit may well end up being the best (or only) way to resolve it.
Whether that justifies a quote of £850+ is a separate point, and I'd certainly recommend getting another quote if at all possible. All RCBO board(s) may be reasonable at that price, while a dual RCD would not IMO.
Some of the errors on the schedule are fairly common (The RCD for fault protection should be N/A but seems to be a very common error).
The main issue that might require a new CU is the lack of RCD to sockets. But the form filling is confusing at best.
5.12 has N/A for mobile equipment for use outdoors, which suggests this might be a higher storey flat? If so, then most of the guidance suggests that lack of RCD for socket circuit is a C3, not a C2.
This may be one where NAPIT strikes again? Though if it where I'd expect there to be a C2 for no RCD on cables <50mm, and instead that is ticked, as is the box for RCD protection for luminaires!
There is also an FI on the schedule for (I assume) the fused spur in the bathroom, but this is given a C3 on the observations - and the only FI there is for grommets missing from back boxes, which is usually not mentioned, or a C3 at worst unless there is actual visible cable damage.
No sure why 4.8 - 'manual operation of circuit breakers and RCDs' is a C2 either, unless one of the breakers didn't isolate, in which case that should be noted as an observation.
Likewise not sure what 'open connectors' for hot water pump means? No earth continuity? Is it a class 1 pump? Presumably if it's working then it has a L and N connection...
It's pretty clear that those IR tests are made up too - almost no chance that they were able to isolate everything on those circuits to get a L/N reading that high.
However, issues with the report aside, Just from what I'm seeing, this is an installation that might be just on either side of 'satisfactory' depending on personal judgement, (if the individual minor issues were fixed), but an installation that will need a new CU in the not too distant future regardless.
So in terms of advice to the OP, although you might be able to find an electrician who would give this installation a satisfactory, it's also possible that someone could do a perfect report and still reasonably find it unsatisfactory.
It may be worth discussing with other electricians and getting them to quote for remedials based on this report, as I think you might be able to get lower than £850. (I don't know what Oxford rates are like though).
Reply to Another EICR RCD question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD...
7K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...