Yep I am with you on that. My notion above is that a switch fuse disconnector is installed then the armour does become a cpc, if not then I would view it as an extension of the earthing conductor. This is all assuming bonding is not required and then the armour only need be sized for its adequacy as a cpc in relation to the protective device at the switch fuse. If bonds are required this is irrelevant.
It is the 4 core 25.0 swa I am a bit confused with, I am assuming it is coming from the DNO source by way of said switch fuse.