Yep I am with you on that. My notion above is that a switch fuse disconnector is installed then the armour does become a cpc, if not then I would view it as an extension of the earthing conductor. This is all assuming bonding is not required and then the armour only need be sized for its adequacy as a cpc in relation to the protective device at the switch fuse. If bonds are required this is irrelevant.
It is the 4 core 25.0 swa I am a bit confused with, I am assuming it is coming from the DNO source by way of said switch fuse.
"542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor." (Note quotation marks)
Irrespective of whether there are extraneous-conductive-parts or bonding conductors, the requirements are for the CSA of the main earthing conductor to be determined by use of Table 54.8, where the earthing conductor is other than copper, the CSA shall afford equivalent conductance. (Note lack of quotation marks)
I am not sure if you are being deliberately obtuse, again or whether you genuinely do not understand!
The DNO supply comes into the green cabinet, and within this cabinet there is a 4w 3ph dist board.
The 4c 25mm SWA runs from here to the garage, to another 3ph dist board, then from here to the house.
There is a duct from cabinet to garage, so an additional bond could be pulled in, but as I say, the incoming water is plastic.
Okay got you now.
My worry is : if the DNO supplies the means of earthing (TNCS) and their cutout and fuse is in the green box at the boundary, then the installation's MET should be there. So if you are using SWA armour from green box to garage then it's insufficient for bonding to the garage too.
Thanks, but if the incoming water is plastic, there is no gas/oil, RSJ's are enclosed, and there is no other exposed metal work, what do you bond to?
Like I said, it would be possible to pull a 10mm in (using the SWA as cpc).
So providing there is no bonding requirements, using the PME earth is ok.
I don't know the specifics, please tell me somebody.
If you have an extraneous conductive part, is it relevant wether it's exposed or not? I would have thought you would have bond it regardless. I certainly would personally.
The garage and house are timber framed, with the rsj in the house resting on timber supports, so not going to have a potential to earth.
My feelings for what they are worth are, pull in another CPC from the incomer position to the garage then onto the house, terminating at each point in a single way service block. This means you have covered all bases, you know what they say assumption is the mother of all ****up's.
Can you 100% guarantee the metal work is enclosed throughout and will remain enclosed?
It would difficult to achieve if the metalwork was extraneous, you often see it partially boxed in for aesthetic purposes or given fire protection but as you say to totally contain it 100% would be all but impossible especially on large structures and not cost effective, you may as well bond it. From what the op says it doesn't sound extraneous.
dmcturk,
Leesparkykent,