I have a situation whereby a new build property has had a green electrical cabinet installed at its boundary, and a new 3ph PME supply installed.
There is a 4c 25mm SWA from here to the detached garage, which will house the plant room (3ph ground source heat pump, 3ph PV inverter), and then another 4c 25mm SWA from the garage to the house.
Incoming water is a new polypipe, and there is no gas/oil on site.
Is there anyway to use the PME, or will I need to TT each site??
Is 3 phase required in the house? Why not install 5c or run supplementary earth along side swa to futureproof any alterations? Is there any exposed structural steel work that is extraneous in house of garage?
Sounds like the cables are already installed.
As long as there are no extraneous parts requiring main bonding in either the garage or house then the PME earthing system can be used.
No.
The requirements for bonding conductors also apply to the main earthing conductors where PME conditions apply.
To my knowledge all pipework in the house will be plastic, but plant room will probably contain copper.
No exposed steels, all rsj's to be boxed in.
House is 3ph in order to to benefit from the 3ph solar PV, and keep it all balanced.
If main protective bonds are required then the armour is inadequate to support the bonding. It is assumed a switch fuse disconnector is to be used at the source of supply, the earthing conductor for this can be selected from Table 54.7 without calculation unless the DNO prescribes otherwise. From here the armour can be used as the cpc (assuming bonding is not required), you can verify the suitability of the armour to be used as a cpc using 543.1.3 and the adiabatic equation, it is not likely this will indicate the armour is not suitable. Remember if bonding is not an issue and a switch fuse connector is in place the armour is a cpc and not an earthing conductor.
"542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor." (Note quotation marks)
Irrespective of whether there are extraneous-conductive-parts or bonding conductors, the requirements are for the CSA of the main earthing conductor to be determined by use of Table 54.8, where the earthing conductor is other than copper, the CSA shall afford equivalent conductance. (Note lack of quotation marks)
On the earthing conductor bit, I've been struggling with this. Opening GN8, page 37, it reminded me "the earthing conductor of an electrical installation is the protective conductor that connects the means of earthing (DNO in this case) with the MET of the installation ... There is only one such conductor in each installation."
So my thoughts are : Assuming the cutout, service fuse and meter are in the garage, then the MET is likely there and the cable linking MET to cutout is the earthing conductor for the whole site. Since we know the DNO incoming is 25mm, the earthing conductor could be selected as 16mm, being the bigger of Tables 54.7 and 54.8, if I've understood correctly. Then the cable from garage to house needs to provide CPC and protective bonding conductor (if required). CPC could be selected from Table 54.7 to be the adiabatic equivalent of 16mm copper, and for this SWA armour is ok. The protective bonding conductor (if required) could be selected from Table 54.8 to be the conductive equivalent of 10mm copper, which the armour does not meet.
Please let me know if I've stuffed this :)
Yep I am with you on that. My notion above is that a switch fuse disconnector is installed then the armour does become a cpc, if not then I would view it as an extension of the earthing conductor. This is all assuming bonding is not required and then the armour only need be sized for its adequacy as a cpc in relation to the protective device at the switch fuse. If bonds are required this is irrelevant.
It is the 4 core 25.0 swa I am a bit confused with, I am assuming it is coming from the DNO source by way of said switch fuse.
I am not sure if you are being deliberately obtuse, again or whether you genuinely do not understand!
The DNO supply comes into the green cabinet, and within this cabinet there is a 4w 3ph dist board.
The 4c 25mm SWA runs from here to the garage, to another 3ph dist board, then from here to the house.
There is a duct from cabinet to garage, so an additional bond could be pulled in, but as I say, the incoming water is plastic.
Okay got you now.
My worry is : if the DNO supplies the means of earthing (TNCS) and their cutout and fuse is in the green box at the boundary, then the installation's MET should be there. So if you are using SWA armour from green box to garage then it's insufficient for bonding to the garage too.
Thanks, but if the incoming water is plastic, there is no gas/oil, RSJ's are enclosed, and there is no other exposed metal work, what do you bond to?
Like I said, it would be possible to pull a 10mm in (using the SWA as cpc).
So providing there is no bonding requirements, using the PME earth is ok.
I don't know the specifics, please tell me somebody.
If you have an extraneous conductive part, is it relevant wether it's exposed or not? I would have thought you would have bond it regardless. I certainly would personally.
The garage and house are timber framed, with the rsj in the house resting on timber supports, so not going to have a potential to earth.
My feelings for what they are worth are, pull in another CPC from the incomer position to the garage then onto the house, terminating at each point in a single way service block. This means you have covered all bases, you know what they say assumption is the mother of all ****up's.
Can you 100% guarantee the metal work is enclosed throughout and will remain enclosed?
It would difficult to achieve if the metalwork was extraneous, you often see it partially boxed in for aesthetic purposes or given fire protection but as you say to totally contain it 100% would be all but impossible especially on large structures and not cost effective, you may as well bond it. From what the op says it doesn't sound extraneous.
South east
Another "exporting PME post"...
dmcturk,
Leesparkykent,