Any recommendations for workable pliable SWA that doesn't need butchering when trying bend and terminate.
 
Last edited by a moderator:
Off the top of my head the closest thing i can think of is SY but doesn't offer the same mechanical protection as SWA.
SY (and CY) are not to any BSI standard, so strictly speaking a risk without assessing their suitability. Also they are not UV tolerant so can't be used outdoors, further limiting where they are suitable.

Using rubber cables like H07RN, or hard plastic like NYY-J, is fine for many situations, but as it lacks both the mechanical protection of the SWA and the earthed shield you may have to put in 30mA RCD protection and that might be a selectivity issue.

However, all cables have a bend radius limit of something like 5-10 times their diameter so if the problem is tight bends then the answer has to be thinner cables (possibly parallel sets), or the cores of SWA bending separately in a box at building entry, etc.
 
The site i'm working on at the minute, they put SWA down some protective conduit, under the ground in conduit, up the garage wall in conduit and then through into the garage, a run of maybe 2 meters total, and it was just to feed one garage socket and one light on a fused spur.

SWA AND conduit seemed very unnecessary but they said that's the way they've been told to do it by the building control guy.
 
Sounds a bit OTT but better to be over engineered than unsafely installed, although sounds like the swa would have been plenty adequate in this case!
Was the 'building control guy' the designer?
 
Sounds a bit OTT but better to be over engineered than unsafely installed, although sounds like the swa would have been plenty adequate in this case!
Was the 'building control guy' the designer?
Probably not, it's all new builds so would have gone through various designers and planners.

For me, conduit serves no purpose there, the steel wires literally do its job already.
 
That is odd.

Duct allows for cable replacement if needed, also gives a little more protection against the odd stone, etc., if badly back-filled. Also not likely to rust!
Aye, i was puzzled to be honest. Just black placcy conduit. Ducting is essential imo but conduit is just odd. I thought it might have been a one off that someone had gotten wrong, but every one of the 80 houses on the estate is like it.
 
It can help prevent tearing the outer sheaf when rough --- bodgers pull it through the wall without a care in the world.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Midlands
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Any recommendations for workable pliable SWA
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
M Lynch,
Last reply from
philectrical,
Replies
23
Views
2,360

Advert

Back
Top