matthunt
all equipment sold in the UK should be rated for that full voltage range.
Similarly all installations including cables, MCBs etc should be sized to be capable of carrying the maximum current that unit can produce at all voltages. If it's not then that's not the fault of solar PV installations, it's the fault of whoever under-specified the cable / MCB in the first place.
If the local grid is going outside the allowable voltage limits due to solar installations, then it probably means those systems inverters haven't been set up properly to G83 protection settings, and the DNO would have the power to require those systems to be disconnected.
btw - the allowable instantaneous voltage limit is 264V, 253 is the maximum 10 minute average voltage.
fwiw, Northern PowerGrid have recently dropped the voltage across their networks by 6V to allow for greater solar PV input / reduce over voltage issues - many of which were actually down to the grid delivering power above the 253 limit prior to the PV being installed anyway.
There will be more and more issues around this, but if installed to current standards the issues should more be around voltage swings around the 253V mark as inverters cut in and out. We're hopefully going to be trialling a system with Northern PowerGrid to resolve this issue by setting the inverters to reduce their output as it approaches the voltage limit instead of just cutting in and out.
Hi Gavin, i think you are missing the point, the higher the voltage level the more power you use, as current is relative to voltage