I am not seeing the point of it all.
AIUI, it's a historical wiring practice, designed to save copper.
Because they have 110-0-110 split phase, you can wire two sockets across the phases with one shared neutral, the maximum neutral current is when one socket is fully loaded. If you load up both sockets then the neutral current reduces. Thus if you are wiring radials to pairs of sockets (double plates), you save one conductor's worth of copper v.s. separate neutrals. Put another way, it needs three wires to have one socket on a radial - with this arrangement, you only need four wires to have two sockets - a 1/3 saving in copper v.s. running two-off three wire radials and both are still separately fused (no fused plugs remember.)
Also AIUI, this was accepted as being fine with separate fuses. From the comments above, it sounds like this is no longer allowed. With a 2-pole linked breaker I'd see nothing wrong.
But, that's not what the OP has drawn (a few years ago

). As drawn, one phase supplies the 1st and 3rd socket pairs, while the other phase supplies the 2nd and 4th socket pairs. Same idea would apply, loads on different phases act to reduce neutral currents, and thus still save on copper.
Don't forget that they use half the voltage, so double the current for everything, so more copper than we'd use for the same power rating of the circuit.
Any fault occurring and all receptacles are off.
But how is that any different to us having a small (sometimes only one) RFC with lots of sockets on it ? I'm assuming this isn't the only set of sockets in the building.
N.B. I have no idea what the regulations (codes) do and don't permit over there.