Planning a layout for new kitchen with (2) two 120‑volt circuits wired with (1) one three‑wire cable connected to a double‑pole circuit breaker. Is this:

A) Allowed
B) Not Allowed

Black powers one circuit
Red powers other circuit
Green neutral serves both
Ground not shown

ps Image doesnt show GFCI which will be used in Kitchen as per code.
pps Does code generally vary in different States
 
@Megawatt another one for you.

we wouldn’t do it in uk. I suppose the same is said for US. The neutral is carrying the load being used by both circuits.
Someone in the future works on the first outlet... isolates it’s breaker and tests it. No power, and starts removing wires. The neutral is also carrying the load from the other circuit, so when they separate the neutral joint, bang flash.

of course, I’m simplifying things... and I suppose that’s why you have wire nuts in the back of the boxes... so you can disconnect the outlet without separating the return path.
 
Pretty picture, but looks a very complicated way of achieving a circuit, aren't straight forward Radials allowed in the US?
 
we wouldn’t do it in uk. I suppose the same is said for US. The neutral is carrying the load being used by both circuits.
But here it appears to be a linked double-pole breaker, in that respect not really any different from a typical three-phase system here where it would be allowed to have single phase loads off it to the common neutral (e.g. lights in factory to reduce strobing).

Had it been separate breakers then a definite NO, as for our "shared neutral" prohibition.

But as you said, one for @Megawatt
 
But here it appears to be a linked double-pole breaker, in that respect not really any different from a typical three-phase system here where it would be allowed to have single phase loads off it to the common neutral (e.g. lights in factory to reduce strobing).

Had it been separate breakers then a definite NO, as for our "shared neutral" prohibition.

But as you said, one for @Megawatt
Agree with this, in the uk we would consider this to be a single circuit although it is multi phase.
The key is the fact it is fed from one circuit breaker, not 2 single pole breakers.

However, it would not be my preferred method of installation for the following reasons.

A fault or overload on 1 set of outlets will trip the power off to both sets.

It would be easy to miss in the future and replace 2 pole breaker with 2 single pole breakers, this would lead to the possibility of a live N when circuit is being worked on and believed to be isolated.

One of the American experts will be better at advising on wiring codes but, in my opinion, the risks are greater than any cost saving or other reward.
 
View attachment 65039
Planning a layout for new kitchen with (2) two 120‑volt circuits wired with (1) one three‑wire cable connected to a double‑pole circuit breaker. Is this:

A) Allowed
B) Not Allowed

Black powers one circuit
Red powers other circuit
Green neutral serves both
Ground not shown

ps Image doesnt show GFCI which will be used in Kitchen as per code.
pps Does code generally vary in different States
First off you are not allowed to share neutrals period. And you didn’t just say the GREEN serves both the neutral and the equipment ground. That is so wrong
 
Must be my eyes, but I'm sure the legend for this drawing should be
Black = L1
Red = L2
White = N
green = ground
As far as the states being different is because every particular state works out of different editions of the NEC. There are states are still working out of the 2014 edition of the NEC. I don’t get it but your state has adopted the 2020 edition of the NEC and so has my state.
 
With AFCI's being required for almost all residential 120V circuits, it makes it very hard, expensive, and sometimes impossible to use multiwire circuits, & some circuits like kitchen small appliance branch circuits also required to have GFCI protection too, 2 pole AFCI's & GFCI's are not as common, although the 2020 NEC that has been adopted by 9 States, at this writing, is now requiring GFCI's for ranges, dryers, A/C condensing units, too now.
 
View attachment 65039
Planning a layout for new kitchen with (2) two 120‑volt circuits wired with (1) one three‑wire cable connected to a double‑pole circuit breaker. Is this:

A) Allowed
B) Not Allowed

Black powers one circuit
Red powers other circuit
Green neutral serves both
Ground not shown

ps Image doesnt show GFCI which will be used in Kitchen as per code.
pps Does code generally vary in different States

I am not seeing the point of it all. Any fault occurring and all receptacles are off. With two single pole breakers , only two of the receptacles / (the circuit) would be off . I view the image as having a white neutral and a green ground with bus bar. I see the equipment ground , but I am not sure what that's in the image.
 
I am not seeing the point of it all.
AIUI, it's a historical wiring practice, designed to save copper.
Because they have 110-0-110 split phase, you can wire two sockets across the phases with one shared neutral, the maximum neutral current is when one socket is fully loaded. If you load up both sockets then the neutral current reduces. Thus if you are wiring radials to pairs of sockets (double plates), you save one conductor's worth of copper v.s. separate neutrals. Put another way, it needs three wires to have one socket on a radial - with this arrangement, you only need four wires to have two sockets - a 1/3 saving in copper v.s. running two-off three wire radials and both are still separately fused (no fused plugs remember.)
Also AIUI, this was accepted as being fine with separate fuses. From the comments above, it sounds like this is no longer allowed. With a 2-pole linked breaker I'd see nothing wrong.

But, that's not what the OP has drawn (a few years ago :rolleyes:). As drawn, one phase supplies the 1st and 3rd socket pairs, while the other phase supplies the 2nd and 4th socket pairs. Same idea would apply, loads on different phases act to reduce neutral currents, and thus still save on copper.
Don't forget that they use half the voltage, so double the current for everything, so more copper than we'd use for the same power rating of the circuit.
Any fault occurring and all receptacles are off.
But how is that any different to us having a small (sometimes only one) RFC with lots of sockets on it ? I'm assuming this isn't the only set of sockets in the building.

N.B. I have no idea what the regulations (codes) do and don't permit over there.
 