ian hall

If you had to change a bathroom light fitting for another (assume correct zone rating) and had to fit an extractor fan(230v)at the same time, would you fit an rcd. Seems to me it,s try and fit an rcbo or an rcd spur or none of the above!!! Obviously the bathroom firm want the lowest invoice possible.

Ian
 
I would allways have fitted a 3 pole fan isolator it just seems alien fitting an rcd for a fan!
The Niceic say that an rcd would not be needed if the light fitting "only" were being changed but the new wiring for the fan will need a minor works which in turn will require an rcd. All agree with that?

Ian
 
So, what do you reckon. Alter the wiring and put an rcd spur in the airing cupboard to cover lights and fan. That would also be means of isolation for the fan ie no need for a 3 pole.
 
either do what you just said or fit a tp fan isolator and change the mcb for a rcbo, whichever is cheapest and easiest if thats what the customer wants
 
You will need to fit a 3 pole isolation switch if the fan has a tmer fitted so that you can isolate the feed, switch wire & the neutral . If you are just fitting a fan without run on timer do it as you said.
 
You will need to fit a 3 pole isolation switch if the fan has a tmer fitted so that you can isolate the feed, switch wire & the neutral . If you are just fitting a fan without run on timer do it as you said.

Does not matter if it has a run on timer or not should fit an isolater next to it anyway.

Besides all of that if you are going to work on the fan you should isolate it at the DB before commencing any work.
 
The rcd spur would isolate the fan too.

Not if its a timer fan , as you have to take permanent L , RCD fuse spare will be fine on a standard fan , but you will need to put in a fan isolator sw as well as RCD protection if you are fitting a timer/humidistat fan .

Ste :)
 
Crossed wires!!!!
The feed would go into the spur then to the light-regular 3 plate connection/timer fan. So all is controlled by spur. Probably best to fit 3 pole too though in case they want light but not the fan
 

Reply to Bathroom fan and light in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock