R

Rosco

Good morning guys and girls
I have attended a kitchen rewire this morning to test a install buy a 3rd party.
The boiler spur is directly above the draining board I'm quite sure this shouldn't be the case. I've been told by the installer that "it's fine it's rcd protected" is this just waffle to get me to sign it off.
Surely it's the same principle as a light switch inside a bathroom?
 
If you are signing off a third party cert, were you not involved at the start of the job ?
There is nothing to say that a FCU cannot be near a draining board, just as there is nothing wrong with a plate switch in a bathroom.

Suitability for the environmental effects likely to be encountered is the reg you have to consider here, and that's your call.
 
If you are signing off a third party cert, were you not involved at the start of the job ?
There is nothing to say that a FCU cannot be near a draining board, just as there is nothing wrong with a plate switch in a bathroom.

Suitability for the environmental effects likely to be encountered is the reg you have to consider here, and that's your call.
The work was done by the kitchen fitters my boss has just sent me to do a test on the whole house.
I personally wouldn't put the spur that close
 
The work was done by the kitchen fitters my boss has just sent me to do a test on the whole house.
I personally wouldn't put the spur that close

Which scheme are you notifying the work through ?
The 2 schemes that I know of that offer third party notification, Napit and Stroma, both require inspection at first and second fix.

You will be signing your name to the fact that you have inspected the cables at first fix and that all is compliant. If you personally are not happy with how things have been done, then don't sign your name to it.
 
We use the nic for all certs our qs deals with all the necessary notifying so wouldnt know, if it's not against regs can I put it as recommendation for improvement?
 
We use the nic for all certs our qs deals with all the necessary notifying so wouldnt know, if it's not against regs can I put it as recommendation for improvement?
I wouldn't see it as appropriate to be recommending improvements on new work!
 
We use the nic for all certs our qs deals with all the necessary notifying so wouldnt know, if it's not against regs can I put it as recommendation for improvement?

Are you there to do a periodic report ?
 
Are you there to do a periodic report ?
Does seem odd, if he's doing an EICR then he shouldn't be concerned about one specific issue, just give an honest appraisal of the whole installation. If he's doing a MWEIC or EIC then he can't be recommending improvements!!
 
Does seem odd, if he's doing an EICR then he shouldn't be concerned about one specific issue, just give an honest appraisal of the whole installation. If he's doing a MWEIC or EIC then he can't be recommending improvements!!
From what I can gather the landlord has asked us for a EICR and has had a new kitchen fitted and new services
 

OFFICIAL SPONSORS

Back
Top