I've not yet got a copy or read the 18th ed
But I heard the other day from a young Engineer at work who's doing the course ( his first time doing regs exam) that in the 18th it's compulsory to bond all joins in tray etc

Can anyone elaborate on this?
 

Ian1981

-
Mentor
Arms
Esteemed
I've not yet got a copy or read the 18th ed
But I heard the other day from a young Engineer at work who's doing the course ( his first time doing regs exam) that in the 18th it's compulsory to bond all joins in tray etc

Can anyone elaborate on this?
The requirement to earth or bond tray is the same as it’s always been
 

edexlab

-
Arms
  • Thread Starter Thread Starter
  • #3
Yes I thought it might be ...

When he mentioned it I asked him what had changed in regard to this , he just said it was a new requirement and in future we'd probably have to do it.

To be fair he's never used BS7671 so I did think that maybe he's mistaken.

In the job I do, we run tray fixed to steel box section frames (powdercoated) and generally it's the customers responsibility to ensure bonding is suitable to that particular countries regs


ie in China and India they do nothing, but other countries have varying amounts of bonding to frame and tray

One company insists we link every single join in tray and bond repeated intervals to all steelwork so in view of this it's always agreed in the contracts that all power supplies and bonding are carried out by a local contractor
 
D

Deleted member 26818

Is the tray extraneous or an exposed conductive-part?
 
Usually there is no need to either earth or bond traywork. If the cabling is insulated and sheathed, Class 2 equivalent construction, the traywork won't be an exposed conductive part so no earthing required. Traywork doesn't usually introduce an earth potential that isn't already present, so no bonding required.

That being said, inspectors love to snag traywork which isn't earthed or bonded.
 

edexlab

-
Arms
  • Thread Starter Thread Starter
  • #8
Heard that argument a couple of times!

One firm I worked with had us go round checking all the tray on a big job with a long lead and test to show the Clerk that the tray continuity was ok , potential to earth was no worse than sll the metal work around the place etc and that bonding at couple of points was sufficient

Still ended up having his way and bonding every thing even after a Chartered Engineer agreed that it wasn't needed
 
T

Toneyz

It makes me wonder what the world these clerks of works and electrical consultants live in the other day I was doing some testing with a contracts manager and the consultant asked if the classroom sink needed bonding they still have in some of these specs about bonding window frames and suspended ceilings.
 
I've not yet got a copy or read the 18th ed
But I heard the other day from a young Engineer at work who's doing the course ( his first time doing regs exam) that in the 18th it's compulsory to bond all joins in tray etc

Can anyone elaborate on this?
Yes true ,it has to be continuous any cut in the tray will hinder that hence you put another link to make it continuous.
 
D

Deleted member 26818

Can anyone quote the Reg. No. that requires tray to be bonded?
Would probably help if we knew whether the tray is extraneous or an exposed conductive-part.
 

edexlab

-
Arms
  • Thread Starter Thread Starter
  • #12
Cables are insulated and sheathed so not an exposed part

Any earth potential is the same as the metal framework and walls that the tray is attached to

So I would say it's neither exposed or extraneous
 

edexlab

-
Arms
  • Thread Starter Thread Starter
  • #14
In this case the whole structure is one big faraday cage
Even where tray joins are bolted together I think there's enough surface area clamped together or fixed to brackets which are fixed via tapped holes all along the length of runs to make the continuity consistent .
 